Finding a reasonable limit switch that can carry 60+ amps reliably will be a challenge. And getting two of them for a low cost will probably not happen. Besides that, the 65 amp wiring to and from the two switches will be a big pain, because at that current #6 wire is used.
So YES, for that circuit the limit switches would be a big problem.
The other rather big problem is that now the motor control relay has become a double pole-double-throw relay with one set of contacts good for at least 65 amps. That is an expensive item, and the application would require two of them.