- 30,680
He did'nt stay long, 15min this AM then dissapeared right after posting!.Boy it sure would be nice if the TS could just clarify that one detail.
He did'nt stay long, 15min this AM then dissapeared right after posting!.Boy it sure would be nice if the TS could just clarify that one detail.
First I wat to go all the way up and down. There is no reason to stop short in either direction. I figured momentary switches woul add a level of safety in the event the limit switch failed. As for the motor it is 12 Vdc. Max draw at lockup is 900 watt. The power supply is rated for 85 ampsWelcome to AAC.
Off to a decent start, but we're going to need some clarification. Do you want to "Push the UP button" and have it go all the way to the UP LIMIT? Or do you want it to go UP only while you're pushing the UP button? There's a difference.
If your goal is to send something to full up position then stop with just a single command then a push button isn't the best way to go. Let me be a little clearer on this: Suppose you are moving a sled from ground level to the second floor. You push the button once and let go while the sled moves all the way up. OR you want to move the sled HALF way up. You push the button and hold it as the sled rises. When it's at the level you want you release the push button? Same would apply to the down command as well.
I understand the desire for the "ON" "OFF" switch, that makes sense. But there are other things to consider as well. Power source is important. If you want to move a heavy load you need a power supply with sufficient power to do the work. So tell us about the motor and the power supply. How many amps does the motor draw at a dead stall and what's the peak amperage at the rated voltage of the supply? Also important is the amperage going through the switches. A small motor shouldn't be a problem for a small push button, but a big motor will burn the switch out.
Are you opposed to doing this with relays? If the switches are small and the load is big then you can use the switches to activate relays that will control the heavy load.
There would be no difference from that point of view, maintained or P.B.I figured momentary switches woul add a level of safety in the event the limit switch failed. As for the motor it is 12 Vdc. Max draw at lockup is 900 watt. The power supply is rated for 85 amps
That will require 100 amp relay contacts and limit switches if wired in series.As for the motor it is 12 Vdc. Max draw at lockup is 900 watt.
And there is a question of how much current the motor requires.
The TS stated:PS = 12V @ 85A
Motor = 900W @stall (75 amps)
No little push button is going to handle that much power.As for the motor it is 12 Vdc. Max draw at lockup is 900 watt. The power supply is rated for 85 amps.
I sited the overhead crane as an example of the need for constant human attendance during operation. The TS doesn't want to push a button once for a moment and have the trolly (or whatever) traverse from full down to full up without the need for attendance. If something requires that big a motor then I would suspect it probably should be under constant human control.First I wat to go all the way up and down.
That's not what I read.The TS wants to push a button once for a moment and have the trolly (or whatever) traverse from full down to full up without the need for attendance.
The chance of the motor locking up or stalling is for all practical purposes “0”. The motor has a 90:1 gear reduction. It will be Turning a shaft winding a strap to lift no more than 100 lbs Think of a winch of sortsThere would be no difference from that point of view, maintained or P.B.
The "Lockup"? is it likely to be stalled?
What is the nature of the load?
Max.
Not necessarily, worm & pinion at 90:1 would normally be inconsequential.But there would still be coasting.
No, limit switches can not control coasting. They can be adjusted to allow for coasting but since it varies with load it is not a constant amount.The location of the limit switches can also control coasting.
I like your design. I have made a change to it to get the limit switches out of the high current path. let me know if this will work. See attached diagram.Using two relays and small PB Switches, this works up to 2 amps motor draw. You can raise or lower (something) to whatever level you like without exceeding the limits. 2 amps because that's how big I drew the PS. In the event you push both UP and DOWN at the same time the motor does nothing. And when the relays are both off (or both on) they can act like a dynamic brake for the motor.
View attachment 226538