That looks interesting. It reminds me of a time when I was very young and my father brought home a really expensive grinder that had stopped working. I checked it out and found the reason it was not working was because it could not start turning. The cap was bad.I like it.
At work today I opened waterpump wiring terminal boxes as I thought, why not test the amperage through each winding. I found the following:
Water pump 1
2.7A through the 20uF Capacitor
3.1A through Live wire
Water pump 2
1.86A through 20uF Capacitor
3.67A through Live wire
Water Pump 3
2.48A through 20uF Capacitor
3.44A through Live Wire
Assuming I've clamped my meter in the correct position which Im almost certain I have, and assuming the motor is basically the same wiring as this diagram than the current though the "Running Winding" would be about 0.4V. Calculated simply by subtracting the current through the cap from the main live wire current. This running winding I thought would actually be drawing more current but perhaps it is not due to having a much larger inductance value.
View attachment 354594
Further info:
- The water pump is rated to run at 4.6A maximum
- The MCB connected is a 10A
I did not have the means to get a new cap back then, so I used a push button. The push button energized one of the windings to get the motor started, then all you had to do is release the button and the motor would wind up to full speed.
Thus we had a pretty nice grinder for almost no cost.
I am not sure though if all motors can run that way. Once the motor starts, the button is released and so the start winding no longer gets any current at all. A cap start motor would normally have some current flowing even after it starts.