MaxHeadRoom
- Joined Jul 18, 2013
- 30,763
One thing to keep in mind if doing it that way is if the open door indicators are using physical outputs of the PLC is to ensure the power to them is kept live when the safety relay operates. Depending on how the safety relay is configured, as normally it shuts off output and control device power.So i can series wire the 22 switches to a single safety relay with one set of the contacts on each sensor and then use the other set of contacts on each sensor to its own input of the PLC which will allow each door its own output alarm or lamp?
It is common to leave the input power on.
Max.