Voltage on my kitchen sink

Thread Starter

SoulCrank

Joined Oct 11, 2016
9
I was checking the outlet above my counter top and it was 122.3 vAC hot to neutral. Just for fun I put the negitive meter lead on my stainless steel sink and it read 20.7 vAC.
Is this because it is gronding through the water? Why only 20 v? It has plastic water supply lines and pvc drain.
 

BR-549

Joined Sep 22, 2013
4,928
It might be crud built up on the inside of drain pipe giving you a path.

You might want to check the conductivity of your water also.

If it was metal plumbing, you should have close to the line voltage between the hot lead to sink.

What was the voltage from hot to ground on outlet?
 

BR-549

Joined Sep 22, 2013
4,928
Adjust a small continuous stream of water. Be very careful........measure between hot lead and water.

And sink and hot lead while water running.

Might consider ground fault outlet.
 

floomdoggle

Joined Sep 1, 2008
217
Do you have copper pipes? You may have the old style grounding to the pipes, usually at the water heater is the connection. While not specifically dangerous, as there is little current draw, a licensed electrician should be your next step.
 
It might be crud built up on the inside of drain pipe giving you a path.
My guess would be that you a little bit of crud which is holding water and some were in the line it comes in contact with earth (metal pipe underground) and it eventually gets to your grounding rods and I'm sure there is a fair amount of resistance causing that drop in voltage.
See if there is a difference after you get rain

AIDayley
 

MaxHeadRoom

Joined Jul 18, 2013
30,585
Also an influence is the high impedance of a electronic VOM. Similar to the neon screwdriver that lights when using ones body as a conductor to earth.
Max.
 

mcgyvr

Joined Oct 15, 2009
5,394
Fluorescent light over the sink? They can easily cause a high impedance meter to show voltage..

But I'm probably going with a high resistance path to ground there through water/moist crud..
 

wayneh

Joined Sep 9, 2010
18,092
Also an influence is the high impedance of a electronic VOM.
I was going to mention that the experiment should be repeated with a high ohms resistor, 100K or 1MΩ for instance, connecting the sink to the ground pin. The tiny current might make the measured voltage disappear. It's just a ghost.
 

Thread Starter

SoulCrank

Joined Oct 11, 2016
9
Adjust a small continuous stream of water. Be very careful........measure between hot lead and water.

And sink and hot lead while water running.

Might consider ground fault outlet.
OK, some things going on. I remeasured everything this morning. 122.0 v hot to n. and hot to g. no dif. ov grd to n. 13.0 v max hot to water flow. Still 20 v on sink while water running. this is a ground fault outlet.
I measured again while dishwasher running. 12.0 v hot to sink, 8 v hot to water, outlet readings were same as above.
 

BR-549

Joined Sep 22, 2013
4,928
Roger on the ground fault outlet. You can track the path down if you want. The resistance between the sink and all structures touching the sink. Then the resistance of the hot water leg, cold water leg and then the drain leg. I believe you said the plumbing was plastic.

Just curious....what kind of soil are you on and are you on a municipal supply or well? Are you on an old sewer system?
 

GopherT

Joined Nov 23, 2012
8,009
Dishwasher and outlet measured are on different breakers.
So you have plastic water pipes to your sink and you measure the stainless steel faucet. What do you expect to be the cause, what happens when you set the meter to current (amps) and measure again, does it blow the fuse in the meter or show a few microAmps of current?
 

wayneh

Joined Sep 9, 2010
18,092
I have to reiterate: A voltage measured without a load is a virtually useless number. If the voltage, say 20V, collapses under the load of a 100K or 1MΩ resistor, it's completely meaningless. So far that's all we've seen?
 

Thread Starter

SoulCrank

Joined Oct 11, 2016
9
Roger on the ground fault outlet. You can track the path down if you want. The resistance between the sink and all structures touching the sink. Then the resistance of the hot water leg, cold water leg and then the drain leg. I believe you said the plumbing was plastic.

Just curious....what kind of soil are you on and are you on a municipal supply or well? Are you on an old sewer system?
It apears to be clayish soil. City water supply, and prob. a very old sewer sytem.

But every thing has changed again. Now I have 102.0 vac hot to sink, 1.3 v gnd to sink 1.2v neu to sink. 117.5v hot to neu.
 

GopherT

Joined Nov 23, 2012
8,009
It apears to be clayish soil. City water supply, and prob. a very old sewer sytem.

But every thing has changed again. Now I have 102.0 vac hot to sink, 1.3 v gnd to sink 1.2v neu to sink. 117.5v hot to neu.
Well, you have just demonstrated that your high impedance meter works like a high impedance meter.

If your sink was in the circuit with the mains power, the sum of the hot-to-sink plus neutral-to-sink would have equaled the hot-to-neutral.

Please measure AMPs from sink to ground. Do you get anything? Likely no.
 