Hey dudes
I'm working on a carton making machine and two contactors have burned out in as many days. The contactors themselves are running two belts one is a simple conveyor and the other is a chain drive, both have overloads and the convery is set for 2 amps and the chain drive 6. Before the contactors burned out (and when i say that i mean the coil is stuck out on both and wont pull in) and the coil is 24vac. I checked the circuitry and it looks like the A2 on them wasnt giving a proper return as when i measured the coil it was only giving 12 amps ac could this under voltage cause the contactor to fail? As in not enough voltage to keep the coil closed and cause it to develop an air gap and fail?
PS all the circuitry on the motors is ok 3 phases in and out and overloads trip when tested
I'm working on a carton making machine and two contactors have burned out in as many days. The contactors themselves are running two belts one is a simple conveyor and the other is a chain drive, both have overloads and the convery is set for 2 amps and the chain drive 6. Before the contactors burned out (and when i say that i mean the coil is stuck out on both and wont pull in) and the coil is 24vac. I checked the circuitry and it looks like the A2 on them wasnt giving a proper return as when i measured the coil it was only giving 12 amps ac could this under voltage cause the contactor to fail? As in not enough voltage to keep the coil closed and cause it to develop an air gap and fail?