Max, you have described a step-down transformer, which provides isolation as a secondary effect. For those applications it is the step-down that is required, the isolation is a free benefit. So that is quite a different situation.There are two methods of using an isolation transformer, one is if you require total isolation from the original (usually mains) supply.
In this case the secondary circuit remains isolated from ground.
The other is where you are for e.g. feeding a control or other circuit from a higher level such as a 3ph supply transformer, in this case, when transformed, the 120v or 240v 1ph control circuit has lost the reference to earth ground, it is then recommended that one side of the secondary is taken to an earth ground point in order to re-reference to earth.
Just as it is done in a residential service supply transformer.
Ref: NEC, NFPA79 etc.
Max.
In this instance we have an isolation transformer added for the sole purpose of providing isolation so that a shock hazard can be avoided.THAT is the sole purpose of the isolation transformer that I use when servicing AC/DC line operated equipment, since an indeterminate mains connection polarity may have the chassis frame at mains potential otherwise. With my isolation transformer in use I could only get a shock by putting both hands where they should not be. AND I have no problem with connecting a scope ground clip to the chassis, which is often tied to one side of the power cord. Of course, it is a good isolation transformer.