It means the transformer is fused for 400mA.Hello. I got this transformer
View attachment 317174
One questión, what does the 400 mA fuse symbol mean? Does the transformer has a internal fuese or this is the fuese recomended for this transformer?
Thank you
best regards
Figure it this way. You have an isolation transformer with a 100 VA (Volt Amp) rating so 100 / 230 = 0.4347 Amp which explains the 0.400 Amp (400 mA) fusing. Normally when transformers like this are fused it is added by the end user. Some include a fuse holder while some need you to add it. All I see in your image is the terminals on the transformer. I assume the addition of a fuse rest with you.One questión, what does the 400 mA fuse symbol mean? Does the transformer has a internal fuese or this is the fuese recomended for this transformer?
Gee, and here I thought they were wound by some guy in Beijing China in his garage. Only the highest in quality and conforming to all transformer specifications. Oh well.But keep in mind that those are higher quality transformers! Produced by an honest company that can be trusted to provide correct information about their products!!