insulation for thick gauge bare wire

#12

Joined Nov 30, 2010
18,224
Wire insulation isn't concerned with current unless you're considering how hot the wire will get.
50 amps, 10 Ga. 1001 ft/ohm
(Let's call it 1000 ft/ohm just to make the math easier.)
For every inch there will be 0.2083 watts.
That inch of wire is bigger than the size of a 1/2 watt resistor, so I guess you're not going to get awfully hot. maybe 50C to 70C, but that's a pure guess based on experience.
I'd say you should be more concerned with the voltage the insulation has to resist.
 

BR-549

Joined Sep 22, 2013
4,928
I don't believe that I have ever personally insulated a wire. They used to have what we called an electrical varnish. You could dip, brush or spay it. I think it was good for 600 volts or such. That was long ago. Sometimes we would apply it to metal chassis to prevent arcing.

I'm sure they have better stuff now.

Search on google.
 

Reloadron

Joined Jan 15, 2015
7,517
A Google of "electrical wire insulation sleeve" will bring up a few dozen examples of insulation sleeve which will work under a wide range of temperatures and voltage breakdown limits. Then for where insulation meets connector there is heat shrink tubing which comes in many flavors so choose what will work for your application.
I am running the device from a 50amp DC current source, not a voltage source.
That's here nor there, depending on the resistance of the device there is a voltage drop across the device and that is the working voltage you need insulation for. With a 50 Amp load you should be able to use light welding cable which is insulated and offers flexibility. A 50 Amp load is not that much and something like AWG 6 or AWG 4 would be more than adequate AWG 6 should be about a 0.182" or 4.62mm diameter and AWG 4 slightly larger so not very thick. You buy your insulation based on Wire OD and insulation ID.

Ron
 

#12

Joined Nov 30, 2010
18,224
I am running the device from a 50amp DC current source, not a voltage source.
Are you saying there is no voltage in the current source?
50 amps times 0.01 ohms = 0.5 volts DC
Why do you consult electronic specialists for insulation that will survive 0.5 volts?
Is that the only consideration for your insulation needs?
If so, any insulation ever invented will be more than enough.
 

profbuxton

Joined Feb 21, 2014
421
!: What length or wire are you trying to insulate
2: What voltage are you using
3: Why are you using bare wire
There is wire commercially available which is already insulated to do what you want( guessing from your post). If you REALLY want to insulate the wire yourself(length unknown) there is sleeving available(heatshrink or silicon). Connectors can be insulated with heatshrink or suitable tape or if you have joints you can use epoxy filled joiners.
 

GopherT

Joined Nov 23, 2012
8,009
I am using this part from lesker to connect to a power supply. The wire is AWG 10 and bare, we want to put some insulation for safety.

http://www.lesker.com/newweb/feedthroughs/power_feedthroughs.cfm?pgid=5kv_cf
part # EFT0543093 ELEC F/T,5KV,30A,(4).094" CU COND,2.75"UHV
Tell me more. I assume this "feed through" from lesker is to pass power into a vacuum chamber (tool) for a deposition process. Is that correct?

If so, I would avoid putting any DIY hardening/curing/drying polymer insulation on the inside of the vacuum chamber because you will never get a decent vacuum if the residual monomer or solvent remains in the polymer (which is hard to avoid). Look for low out gassing materials. Also, most vinyl or polyurethane tubing insulation will out gas forever and you'll never get a good vacuum needed for CVD/PVD / e/beam or whatever type of experiment requiring such a flange.

10 wag wire is not going to bounce around and get tangled - it will stay where you put it.

For outside the chamber, assuming that is how you are using it, almost any "sleeve" material will work (see " heat sharing tubing" suggested above. You can also use rubber tubing or vinyl tubing from the chemistry lab. You have no risk of arc/spark at the single-volt or sub-volt supply you are working with. Also, if you do get a dead short, your "current supply" will limit current (keep current at same value) anyhow
.
 

Kermit2

Joined Feb 5, 2010
4,162
Teflon plumbers tape would fit the bill if temps are under 500F.

Can be easily taken off and quickly re-applied, and is pretty much chemically inert.
 

drc_567

Joined Dec 29, 2008
1,156
There is a product called split loom ... It is a flexible plastic covering that is easily installed and removed. ... Can be stabilized by using an occasional wire tie. ... Comes in different diameters ... Purchase by the foot, at various auto parts stores.
 

Reloadron

Joined Jan 15, 2015
7,517

Tonyr1084

Joined Sep 24, 2015
7,900
I used to do some Hi-Pot testing (High Potential). That means you apply a high voltage to two wires and measure the cross bleed between them. That evaluates the resistive capability of the insulation between the wires.

Funny, you ask about insulation on a bare wire. Bare wire you say? OK, I get it now. You want to add insulation to a bare wire so it's no longer bare. Like others are saying, we need to know the voltage. And then maybe someone here will know the answer. I know I sure don't.
 