Just so we are all on the same channel, back in post #5 I provided a link with timing relay definitions. So your first relay is a delay on make correct?
Upon application of input voltage, the time delay (t) begins. At the end of the time delay (t), the output is energized. Input voltage must be removed to reset the time delay relay & de-energize the output.
Your second relay is an Interval On correct?
Upon application of input voltage, the output is energized and the time delay (t) begins. At the end of the time delay (t), the output is de-energized. Input voltage must be removed to reset the time delay relay.
I see you just posted as I typed. Each relay coil needs to have its rated voltage. If a coil voltage is 120 VAC, 220 VAC, 12 VDC, 24 VSC or whatever it is that's what it needs. You can't place relay coils in series.
Ron
Upon application of input voltage, the time delay (t) begins. At the end of the time delay (t), the output is energized. Input voltage must be removed to reset the time delay relay & de-energize the output.
Your second relay is an Interval On correct?
Upon application of input voltage, the output is energized and the time delay (t) begins. At the end of the time delay (t), the output is de-energized. Input voltage must be removed to reset the time delay relay.
I see you just posted as I typed. Each relay coil needs to have its rated voltage. If a coil voltage is 120 VAC, 220 VAC, 12 VDC, 24 VSC or whatever it is that's what it needs. You can't place relay coils in series.
Ron