Another point is which regulations it has to pass:
A UK Spec emergency lighting unit has to be able to run off its batteries for 3 hours and charge back up again in 12 hours. So its charger has to be rated about 25% of the inverter,
A continental Europe spec emergency lighting unit has to run off batteries for 1 hours and charge back up within 12 hours. So its charge rating is about 8% of the inverter.
Some UPS units have only to power the load for a few minutes whilst whatever it is protecting shuts down properly, and probably can take 12 hours to recharge. So the charger rating is even less.
For chargers rated <10% of the inverter rating, it may well be cheaper to produce a complete charger separate from the inverter rather than involve the extra complexity.