OK I got it working. It's like you said, with the only difference is that I disconnected the com0 to 0v that I had, and with the fact that this is an npn sensor.The way I have it set up in this last picture works with the NPN sensor. This same set up does not work with the PNP sensor.If you have it set for a sinking input which it appears you do.
Then normally you use a sourcing sensor, which a PNP is.
Max.

That's what I uploaded that the PNP(I guessed) sensor providing the current source to a PLC sink input.and a sourcing input must connect to a sinking plc;
That's the second circuit in your posted #70.If a sensor is sinking, it needs the power from the sourcing plc so that the sensor can sink it,
The two NPN type shown below, you can see the current direction(arrow) and the blue line.So what I wish to clear up is, why if my sensor (the one that worked) is npn (sinking), did it work with a npn sink type plc? According to the manual it's a sink type plc:
It is not a language problem, that was a technical issue, as you can see my posted #71 already mention that, I had try other brand (world famous but from other country) that had RS-232 communication code error in the user manual and that was in Taiwan.I have become used to the fact the hard way that not all Chinese instructions are clear or even correct, they consistently issue very confusing instruction details, not at all always correct, not sure if it is always ignorance of the subject or a language problem!.
Max.
I just shown the blue line, but they didn't connected together, It means that you can't connect them together directly for two Sinking type as NPN, the same reason that you can't connect two Sourcing type as PNP.Scott
In that diagram you have current flowing in 2 different directions; from the Blue wire to X0 and at the same time from the blue wire to Vo. How is that possible?