Today I encountered a faulty 400A/200kW contactor (datasheet attached).
The system and contactor work as follows: 230VAC control circuit comes on after power-on and goes to many devices, including this contactor (on terminals A1 and A2, typical nomenclature for the coil) but the contactor does NOT energize (by design) when 230V is applied to A1 and A2. The contactor does not energize until a separate 24VDC signal is applied to another pair of terminals on the coil labeled "PLC". My initial assumption about the reason for this, was that some designers prefer to use 24VDC I/O for everything, so a contactor with 24V coil would be desired, but a 24V coil of this size would draw far too much current for a PLC output. So this is a hybrid that's actually using a 230V coil, which is controlled one level higher by 24VDC. Essentially an embedded interposing relay.
The issue was as follows: when 230V control power is energized the breaker immediately trips. There was a <0.2ohm short across the control circuit which I traced to this contactor on the A1/A2 terminals. When the contactor is disconnected, issue is gone. I placed an order for a new contactor but with several days lead time and production pressure from on high, I was encouraged to "find another (temporary) way."
I dissected the contactor and found a PCB inside with way more components than I expected. I only expected a small relay as I said. But something else was going on here. I could not make out what was going on because the board was thickly potted and only some ferrites and snubbers were distinguishable. Only slightly daunted, and with nothing to lose really, I decided to test my initial assumption.
I am just wondering if anyone here knows that my theory about the role of this PCB is correct or knows it is not. Or if anyone has any more likely speculation as to what this PCB does. But if speculation is offered please identify it as such.
The system and contactor work as follows: 230VAC control circuit comes on after power-on and goes to many devices, including this contactor (on terminals A1 and A2, typical nomenclature for the coil) but the contactor does NOT energize (by design) when 230V is applied to A1 and A2. The contactor does not energize until a separate 24VDC signal is applied to another pair of terminals on the coil labeled "PLC". My initial assumption about the reason for this, was that some designers prefer to use 24VDC I/O for everything, so a contactor with 24V coil would be desired, but a 24V coil of this size would draw far too much current for a PLC output. So this is a hybrid that's actually using a 230V coil, which is controlled one level higher by 24VDC. Essentially an embedded interposing relay.
The issue was as follows: when 230V control power is energized the breaker immediately trips. There was a <0.2ohm short across the control circuit which I traced to this contactor on the A1/A2 terminals. When the contactor is disconnected, issue is gone. I placed an order for a new contactor but with several days lead time and production pressure from on high, I was encouraged to "find another (temporary) way."
I dissected the contactor and found a PCB inside with way more components than I expected. I only expected a small relay as I said. But something else was going on here. I could not make out what was going on because the board was thickly potted and only some ferrites and snubbers were distinguishable. Only slightly daunted, and with nothing to lose really, I decided to test my initial assumption.
- I broke loose the coil ends from the epoxy and soldered on extension wires, ran to the exterior of the contactor. Reassembled the contactor.
- Outside the contactor I installed a 24VDC relay. PLC energizes the relay, relay sends 230V inside to the coil, completely bypassing the PCB.
- That didn't work. Coil just hummed. So I assumed there must be a rectifier in the PCB.
- I installed a diode between the relay and the coil, half-wave rectifier to give it low-stress DC test. That didn't work. Again coil just hummed.
- I reversed the diode.That didn't work. Again coil just hummed.
- I made a full bridge rectifier out of 1N4004 diodes and put it between the relay and coil. THIS WORKED. The contactor pulled in immediately and stayed in, no humming.
- It worked for under a minute and then the coil started billowing smoke.
I am just wondering if anyone here knows that my theory about the role of this PCB is correct or knows it is not. Or if anyone has any more likely speculation as to what this PCB does. But if speculation is offered please identify it as such.