How come I can touch the neutral bus?
ulms
Joined Mar 19, 2024
194
Here is another thing bothering me. This has been unresolved in my mind for 40 years. I have done a lot of work inside of electrical panels (US 240 VAC 1p). I'm looking at the black wire, the so-called hot (L1) coming out of a single pole 20A breaker. It is daisy chained to 5 outlets (in parallel) which may have a lamp or a drill motor a toaster or whatever plugged into them at any given time. After the last outlet in this circuit the white wire, so-called neutral (using 12 AWG NM) comes back to a bus bar in the bonded main electrical panel. I have never intentionally touched that black wire coming from the breaker. I can touch that neutral/ground bus without issue. My question is, if this AC current is going from a max positive to a max negative, a direction reversal, shouldn't that neutral wire shock me depending on where it is in its AC cycle. Doesn't the neutral become so-called hot for half of that sine wave?
BobTPH
Joined Jun 5, 2013
11,666
You have to have connections to two different potentials in order for current to flow. When you touch live, the other potential is ground (earth), through your feet, and you get a shock. Neutral is at the same potential as ground, so there can be no current flow from the neutral bus to ground through your feet.
ulms
Joined Mar 19, 2024
194
Bob, for argument's sake, I'm standing on my concrete floor and I'm touching the neutral bus which at times becomes "hot" but so does the floor?
ulms
Joined Mar 19, 2024
194
Bob , I think you helped me clear this up in my mind. Regardless of the current direction (as determined by the sine wave) I'm "always" at the same potential as the neutral?
MaxHeadRoom
Joined Jul 18, 2013
30,876
View the supply without any earth conductor connection, The supply changes polarity twice each cycle. There is no difference between either conductor where voltage is concerned.
In your case one is bonded to earth.
ulms
Joined Mar 19, 2024
194
Max, if there was no earth conductor, no bonding. I would get zapped touching the neutral?
MaxHeadRoom
Joined Jul 18, 2013
30,876
Yes. The neutral is identical to the 'live' conductor, just that is is 'neutralized' against shock by being connected to earth, in every other respect, it is identical to the 'live' phase.
In any AC supply, any conductor can be connected to earth, in order to provide a neutral.
In other parts of the world thjat use one phase of a three phase supply domestic residences are supplied with a earthed star point of a 3ph transformer, same principle and effect.
Jon Chandler
Joined Jun 12, 2008
1,658
Based on comments here, I suggest you stop poking around inside breaker panels.
Please take a minute to understand this. If you disconnect the neutral (white) wire from the neutral bar, and touch that disconnected white wire and neutral or ground, you WILL receive a potentially fatal shock. The entire load on that circuit will be attempting to take a shortcut through your body.
ulms
Joined Mar 19, 2024
194
Wow, I did not know that. I thought neutral was earthed at the power plant. Thanks for that information.
Ya’akov
Joined Jan 27, 2019
10,356
If instead of you body you put a DMM between a conductor and something else (another phase, the grounded conductor, the earth, &c.) You are measuring the potential between those two points. If you touch the neutral and don't get a shock it means there is no (or very little) potential between you and that point.
Now imagine you have a perfectly operational radar speed gun and you point it at a mountain reading 60MPH. The radar gun is completely in order. How can the mountain be moving at 60MPH?
MaxHeadRoom
Joined Jul 18, 2013
30,876
In NA domestic supply It is grounded at the centre tap of a 120v-0-120v local tranformer secondary .
In other jurisdictions, the local 3ph transformer has a delta connected secondary and the neutral-star point is connected to earth.
ulms
Joined Mar 19, 2024
194
Yes that I am aware of. At first I thought you were talking about the bare copper that comes into the panel with l1 and l2.
SamR
Joined Mar 19, 2019
5,542
The Neutral bus should NOT be HOT. That tells me that even if no one circuit is tripping its breaker that the total load for all of the circuits together is overloading panel. Warm possibly, but not hot! What is the rating of the mains breaker? And what total load is the panel rated for? Something sounds off... If you can, thermal image the panel with the cover plate removed.
ulms
Joined Mar 19, 2024
194
Sam I am not having any electrical problems here. I'm just trying to understand AC electricity, I used my panel box as an example, what I was trying to figure out is if the voltage and current go back-and-forth 60 times per second why doesn't my white neutral wire become like the black L1 wire for half of the cycle and electrify the main panel. ElecSpidey in post #6 may have clearified this for me.