i have a circuit having 20 amps branch breaker, the voltage is 220 single phase, how many sockets i can connect to it. i need to know the quantity once the sockets are connected in loop.
Unless all the plugs have their own fuse, of course.Note that each outlet receptacle should be rated to whatever the circuit breaker is rated to, so that the breaker is protecting each receptacle against overload. You don't want a 15A receptacle 'protected' by a 20A breaker. Same for the wiring, of course.
Wow, really? Never heard that.Unless all the plugs have their own fuse, of course.
(UK local regulation)
That's not entirely true, at least in the USA. It's very common to have 15 amp receptacles on 20 amp / 120 volt branch circuits.Note that each outlet receptacle should be rated to whatever the circuit breaker is rated to, so that the breaker is protecting each receptacle against overload. You don't want a 15A receptacle 'protected' by a 20A breaker. Same for the wiring, of course.
That's true, for a circuit with multiple outlets. Other parts of the code protect against actually plugging a 20A load into a 15A rated receptacle by mistake.That's not entirely true, at least in the USA. It's very common to have 15 amp receptacles on 20 amp / 120 volt branch circuits.
I also have 15 amp outlets on a 20 amp service. Have seen that all my life. Only time I've seen 20 amp outlets has been in professional kitchens where someone may plug in some kind of industrial appliance that actually takes 20 amps. There isn't one thing I own that takes more than 15 amps. My wife's hair dryer is rated at 1500 watts on high. That's 13.6 amps at 110 VAC or 12.5 amps at 120 VAC. Her biggest kitchen appliance draws only 12 amps, so any typical load in the average US home is not likely going to exceed 15 amps.That's not entirely true, at least in the USA. It's very common to have 15 amp receptacles on 20 amp / 120 volt branch circuits.