A transformer:
-50KVA
-11000/220V 50Hz
-NO load 0.3Amps
-No Load losses = 650W
determine;
a)
i)iron loss current. = 59.1mA
ii)magnetizing current = 294mA
iii)no load pf. = 0.201
b) a s.c. test gives Zeq =125Ω ref. to primary
and full load Power losses = 850W
determine:
i) full load sec current = 227.275Amps
ii)efficiency with 70% full load and 0.8 pf lagging = 97.41% (not sure)
iii) the regulation for the condition of b ii)
My problem is that I'm not sure if i should consider Inot(no load component) in part a) to workout b ii) and where to apply the 0.8 pf lag.