Current sensor

Thread Starter

pjreijiri

Joined Aug 19, 2015
116
Hello,
I am working on a device that measures AC current in a wire and then turns on a relay that turns on more devices.
I have been using this:
https://www.alibaba.com/product-det...pm=a27aq.27095423.1978240560.1.78372277WVXPSd

but a lot of them keep breaking down and the output starts flickering. Any suggestions? Maybe I am doing something wrong or if there is a better solution.

I tried to adjust the sensitivity but always the same problem.
 

dendad

Joined Feb 20, 2016
4,634
Have you looped the power wire through the current transformer a few times?
That will increase the signal so it will not be so sensitive.
And I think the sensor output is just a relay contact so the extra relay may not be needed if your load is not too big. It looks to have a contact rating of 300mA. If larger is needed, than use an external relay but make sure the curretn is enough.
 
Last edited:

B-JoJo-S

Joined Jan 3, 2026
210
but a lot of them keep breaking down and the output starts flickering. Any suggestions?
Quick question (observation): Looking at Panic Mode's circuit (post #5) and considering your system keeps breaking down; do you have Diode D3 across the coil of the relay. as shown in panic mode's diagram?
Screenshot 2026-02-26 at 10.37.57 AM.png
 

B-JoJo-S

Joined Jan 3, 2026
210
So K1 & K2 constitute a normally open switch. When current is below a threshold the switch remains open. When current exceeds that threshold then the switch closes. What's the relay for? Are you controlling something that is higher power than the K1/K2 switch can handle? It appears the switch can handle 300mA (0.3A) AC or DC. So maybe you Do need a relay.
Screenshot 2026-02-26 at 10.53.02 AM.png

The following wire diagram suggests it can handle more than 300mA. But I don't know how much current a Contactor would draw. Small electric fan - that's less than 300mA. A relay coil might be below 300mA.
Screenshot 2026-02-26 at 10.52.16 AM.png
But if you're switching an inductive load then you need D3 across the relay coil pointed exactly the way shown. Cathode to the positive rail.
 

Thread Starter

pjreijiri

Joined Aug 19, 2015
116
So K1 & K2 constitute a normally open switch. When current is below a threshold the switch remains open. When current exceeds that threshold then the switch closes. What's the relay for? Are you controlling something that is higher power than the K1/K2 switch can handle? It appears the switch can handle 300mA (0.3A) AC or DC. So maybe you Do need a relay.
View attachment 363962

The following wire diagram suggests it can handle more than 300mA. But I don't know how much current a Contactor would draw. Small electric fan - that's less than 300mA. A relay coil might be below 300mA.
View attachment 363963
But if you're switching an inductive load then you need D3 across the relay coil pointed exactly the way shown. Cathode to the positive rail.
I have probably around 1-1.5Amp load, that's why I am not using it directly.
So you are saying to add a diode between K1 and K2? (K1 and K2 are attached directly to the relay)
https://www.digikey.com/en/products/detail/american-zettler/AZ2280-1A-120AEF/12171666

If yes, what would be the suggestion for picking the part?
 

panic mode

Joined Oct 10, 2011
4,864
300mA rating for a relay output is quite low. even tiny signal relays with gold plated contacts are usually rated for 1-2A. they probably use some tiny SSR as relay. many of those are only good for 300mA.
if it is the output that fails, i would simply use an interposing relay. then the load current for current sensor output contacts will be low. interposing relay contacts can be 10-25A which is more than enough suitable to drive contactor, fan etc.
 

panic mode

Joined Oct 10, 2011
4,864
I have probably around 1-1.5Amp load, that's why I am not using it directly.
So you are saying to add a diode between K1 and K2? (K1 and K2 are attached directly to the relay)
https://www.digikey.com/en/products/detail/american-zettler/AZ2280-1A-120AEF/12171666

If yes, what would be the suggestion for picking the part?

if you are using current sensor to drive that relay, you need to match the circuit type. that relay has AC coil for 120V. since circuit is AC, do not use any diodes. in AC circuits suppression need to be not-polarized, such as MOV or RC. i would not worry about that since coil uses very little power (<3VA).
 

B-JoJo-S

Joined Jan 3, 2026
210
Screenshot 2026-02-26 at 12.51.52 PM.png
Looking at the above we see a rectangle with AC/DC as a power source. The switch merely turns on or off via SSR whatever is being controlled. If the load is greater than 300mA then an intermediate relay is needed. If it's running on DC then you need the diode shown in post #5, Diode D3.
Back in post 5 panic mode drew a DC circuit running on 12V. However, we don't yet have a clear picture of the latch that is being switched or what type and voltage the solenoid lock latch is.
Direct question: What is the voltage of the latch? Is it AC or DC or either? If you know the current draw of the latch, please share that with us as well.
So far we're guessing at whether it's 110VAC or 12VDC and a guess is as good as a stick of dynamite. It can blow things up.
 

panic mode

Joined Oct 10, 2011
4,864
so maybe add another relay between the current sensor and the relay mentioned above (AZ2280-1A-120AEF)?
if the current sensor is driving relay mentioned above (AZ2280-1A-120AEF), no additional "in-between" relay is needed.

current sensor can drive load up to:
120VAC * 0.3A = 40VA
but coil of AZ2280-1A-120AEF only consumes less than 3VA
 

ronsimpson

Joined Oct 7, 2019
4,646
I don't know how this current sensor was designed. I built one using this type of SS relay.
I do not see it in the data sheet, but I believe if you over drive the LED, it emits less light until will becomes "flakey".
1772145612156.png
 

dendad

Joined Feb 20, 2016
4,634
Have you tried looping a number of turns through the current transformer to increase the signal level as I mentioned earlier? Or do you just have the wire trough once?
 

MisterBill2

Joined Jan 23, 2018
27,164
There have been in the past year at least two threads with the same question, and a lot of good suggestions that work. So a bit of research should find those threads.
 