Let's try again:
L1 and L2 - We know what these are.
Ground - I'll define it as the third prong of an outlet. It only carries fault currents. It's an ersatz reference.
Earth - The reference, the ground rod
neutral - Carries current, for 240 V split phase, carries the difference 120 phase currents.
The house needs only one reference. Earth. So, ground goes to earth and neutral goes to earth at only one place.
The telephone protector goes to earth, the copper water lines go to earth, the cable TV goes to earth.
Earth is the reference.
You add a subppanel in an attached section of the house. The sub-panel (main lug) ets modified so the ground neutral bond is removed.
Extra ground lugs are added.
Neutral, ground, L1 and L2 are totaly separate wires. There is no connecton to neutral/ground/earth in thqt sub-panel. Those connections occur at the main panel only.
if you have an external generator, bring it into the system LIKE a sub-panel feed. Separate neutrals, separate grounds, NO EARTH.
Earth will connect to ground/neutral at the MAIN Breaker panel. Everyone is happy, ONE REFERENCE.
Lets connect the water pipes to earth and the CATV to earth like its supposed to be.
Now, lets do some wierd wiring. Three daisy chained outlets to a single breaker, one on each floor. Let's let lightning strike the third floor outlet.
So, anthing connected to floor 2 and floor 1, gets an elevated ground and may have problems. It will raise the potential of thet ground rod. BUT who cares. All other wiring in the house references that reference and those circuits would not be affected. Even the CATV reference would not get affected.
Two grounds, one at the generator and one at the ground rod. Your asking for trouble.
How do I hook up an orange receptacle? https://spyrkaelectric.com/heres-what-you-need-to-know-about-an-isolated-ground-receptacle/
Hospitals mess whatever you learned totally up: https://www.ecmweb.com/bonding-amp-grounding/primary-care-electrician
L1 and L2 - We know what these are.
Ground - I'll define it as the third prong of an outlet. It only carries fault currents. It's an ersatz reference.
Earth - The reference, the ground rod
neutral - Carries current, for 240 V split phase, carries the difference 120 phase currents.
The house needs only one reference. Earth. So, ground goes to earth and neutral goes to earth at only one place.
The telephone protector goes to earth, the copper water lines go to earth, the cable TV goes to earth.
Earth is the reference.
You add a subppanel in an attached section of the house. The sub-panel (main lug) ets modified so the ground neutral bond is removed.
Extra ground lugs are added.
Neutral, ground, L1 and L2 are totaly separate wires. There is no connecton to neutral/ground/earth in thqt sub-panel. Those connections occur at the main panel only.
if you have an external generator, bring it into the system LIKE a sub-panel feed. Separate neutrals, separate grounds, NO EARTH.
Earth will connect to ground/neutral at the MAIN Breaker panel. Everyone is happy, ONE REFERENCE.
Lets connect the water pipes to earth and the CATV to earth like its supposed to be.
Now, lets do some wierd wiring. Three daisy chained outlets to a single breaker, one on each floor. Let's let lightning strike the third floor outlet.
So, anthing connected to floor 2 and floor 1, gets an elevated ground and may have problems. It will raise the potential of thet ground rod. BUT who cares. All other wiring in the house references that reference and those circuits would not be affected. Even the CATV reference would not get affected.
Two grounds, one at the generator and one at the ground rod. Your asking for trouble.