Certainly it is difficult to discover "what changed", and even more challenging when the problem has existed for some time, and probably others have been involved, possibly making changes that are not obvious and not documented.
AND, I am guessing that the machine is in fairly constant use, so an investigation of EVERY CONNECTION is not a reasonable option.
Using a clamp-on ammeter to examine the current balance between phases can reveal a poor connection, and that has allowed me to solve a problem. Checking the current in the ground wire connections, and comparing that with other machines, may also reveal a problem.
I am aware that in some organizations there are rules forbidding any electrical access to any machine electrical system while the machine power is present. Certainly these checks should not be done without another person standing by who knows and is able to rescue another who is being shocked. AND PPE is appropriate for this sort of checking.
AND, I am guessing that the machine is in fairly constant use, so an investigation of EVERY CONNECTION is not a reasonable option.
Using a clamp-on ammeter to examine the current balance between phases can reveal a poor connection, and that has allowed me to solve a problem. Checking the current in the ground wire connections, and comparing that with other machines, may also reveal a problem.
I am aware that in some organizations there are rules forbidding any electrical access to any machine electrical system while the machine power is present. Certainly these checks should not be done without another person standing by who knows and is able to rescue another who is being shocked. AND PPE is appropriate for this sort of checking.