Hello,
I’m looking for insight from those experienced with ABB ACS800 drives, VFD grounding, or EMI/EMF issues.
I’ve been troubleshooting a persistent issue on an extrusion auxiliary drive (auger crammer/feeder motor) and have now ruled out mechanical, process, motor, drive hardware, PLC logic, and tuning. At this point I strongly suspect grounding, shielding, or EMI coupling, and I’m hoping for guidance on further diagnostics.
System Overview (Generalized):

Core Symptoms
What Has Been Ruled Out
Mechanical / Process
Motor
Drive / Power
Control PLC
I logged and livestreamed drive feedback at 8–9 Hz effective sample rate about torque percentage:
FFT Results
A strong, narrow frequency component consistently appears at ~0.336 Hz (~3-second period)
Only Avenue I Have Not Investigated: Grounding / EMI
My mind has began to wonder about common-mode noise, shield termination, grounding topology, or EMI affecting the drive’s torque estimator, rather than true mechanical torque. But I'm not really too sure where I would start for debugging.
I am very open to any feedback and can gladly reciprocate feedback. This has been an ongoing issue for over a decade at the plant I work at and my ops team is considering doubling the motor's output power (same gear ratio) as a solution, but I'm pretty confident that wont solve the problem, just crutch it.
Thank you
I’m looking for insight from those experienced with ABB ACS800 drives, VFD grounding, or EMI/EMF issues.
I’ve been troubleshooting a persistent issue on an extrusion auxiliary drive (auger crammer/feeder motor) and have now ruled out mechanical, process, motor, drive hardware, PLC logic, and tuning. At this point I strongly suspect grounding, shielding, or EMI coupling, and I’m hoping for guidance on further diagnostics.
System Overview (Generalized):

- Drive: ABB ACS800
- Motor: ~5 HP induction motor (multiple motors tested)
- Application: Feeder / crammer auger for an extruder
- Control Mode: Speed control (DTC)
- Gearbox: Fixed ratio (44.71)
- Crammer generally operates only when extruder is running, however results are the same in 'local' mode
- There is an otherwise identical extruder line nearby, and on the same switch gear that runs without issue
Core Symptoms
- The drive reports unstable and elevated torque feedback, especially upon start up and under load. If the motor and gearbox do not have an applied load, the torque% varies by +/- 4% where the nominal torque% varies between 10-14% continuously, even with the motor being fully decoupled from the gearbox
- Torque frequently exceeds 100% and occasionally 150% during applied load startup/ transient periods. The erratic behaviors often trigger torque-based logic.
- Based on all evidence, I do not believe these torque levels represent real mechanical load.
What Has Been Ruled Out
Mechanical / Process
- Auger removed → issue persists
- Motor run completely no-load
- No flight-to-wall contact
- No material present
- No process surging (verified via melt / head pressure)
- Identical system operates normally
Motor
- Multiple motors tested
- Same behavior under no load
- Problem does not follow the motor
Drive / Power
- Drive swapped → no change
- VFD motor cable replaced → no change
- Ran in local mode → no change
- Motor data verified
- MAG ID performed
- Speed tuning reviewed
- PI gains adjusted live → response changes but instability remains
- No drive faults present
Control PLC
- Speed command verified stable
- No dithering or oscillation in reference
- Logic identical to the good line
- Forced parameter value → no change (this was the ultimate proof that it was unrelated to plc logic)
I logged and livestreamed drive feedback at 8–9 Hz effective sample rate about torque percentage:
FFT Results
A strong, narrow frequency component consistently appears at ~0.336 Hz (~3-second period)
- The spike is repeatable across multiple datasets about the same parameter
- The frequency does not scale with mechanical speed
- Melt / head pressure does not show the same oscillation
- Suggests a stable limit cycle, not random noise
Only Avenue I Have Not Investigated: Grounding / EMI
My mind has began to wonder about common-mode noise, shield termination, grounding topology, or EMI affecting the drive’s torque estimator, rather than true mechanical torque. But I'm not really too sure where I would start for debugging.
I am very open to any feedback and can gladly reciprocate feedback. This has been an ongoing issue for over a decade at the plant I work at and my ops team is considering doubling the motor's output power (same gear ratio) as a solution, but I'm pretty confident that wont solve the problem, just crutch it.
Thank you