You have a very common problem people hook the outlet up using the 4 holes in the back 2 things happen the wire gets hot the spring get's weak then the wire arc's and now you have home made resistors you all ways see this more on the ground and the neutral side.
Just find the first outlet that's feed from the breaker box and install new ones on all that's on the same breaker.
99 out 100 times that fixes it that one time it don't you have a cut hot wire that is barely touching and the carbon from arcing has made it to where it's now dropping the voltage
Now if your house was wired using the same power to pickup a light then there can be a wire-nut problem but that more rare then the plugged in outlets causing this.
Space heaters really do a number on outlets that are not installed right
Just find the first outlet that's feed from the breaker box and install new ones on all that's on the same breaker.
99 out 100 times that fixes it that one time it don't you have a cut hot wire that is barely touching and the carbon from arcing has made it to where it's now dropping the voltage
Now if your house was wired using the same power to pickup a light then there can be a wire-nut problem but that more rare then the plugged in outlets causing this.
Space heaters really do a number on outlets that are not installed right