120v AC circuit problem: Plug tester shows OK; multimeter shows only 60v. Why & how to fix?

be80be

Joined Jul 5, 2008
2,396
You have a very common problem people hook the outlet up using the 4 holes in the back 2 things happen the wire gets hot the spring get's weak then the wire arc's and now you have home made resistors you all ways see this more on the ground and the neutral side.

Just find the first outlet that's feed from the breaker box and install new ones on all that's on the same breaker.
99 out 100 times that fixes it that one time it don't you have a cut hot wire that is barely touching and the carbon from arcing has made it to where it's now dropping the voltage

Now if your house was wired using the same power to pickup a light then there can be a wire-nut problem but that more rare then the plugged in outlets causing this.

Space heaters really do a number on outlets that are not installed right
 
Last edited:
Specifically:

1. When the outlet is either (a) the LAST outlet in a chain or (b) the ONLY outlet on the circuit, then the ground connection CAN BE made with just a single long ground wire by first looping that wire under (and tightening down) the box ground screw so that about 6" of that ground wire extends away from that box ground screw; then loop the end of the remainder of that ground wire and place that loop under (and tighten down) the outlet box ground screw. That way, each of the box and the outlet has a securely screwed down (thusly "separate") ground wire connection, beginning with the box.

2. When the outlet is in a daisy chain and is NOT the final outlet, the ground wire coming into the box still can be looped under the tightened ground screw of the box (as described above), but the remaining 6" extension of that ground wire does not get attached directly to a device and, instead, that remaining extension of the ground wire must be twisted together with one end from each of two other "ground" wires: (a) the ground wire in another cable (going back out of the box to the next device in the daisy chain); and (b) a pigtail wire, the other end of which will be looped and placed under the ground screw of the outlet before that screw is also tightened down. This also gives each of the box and the outlet a securely screwed down (thusly "separate") ground wire connection, again beginning with the box.

Is all that correct?

Twisting is NOT sufficient as I have painfully learned.

With a breaker. two wires are not allowed to share the breaker screw. You have to PIGTAIL if you wanted to serve two circuits.

Same with the ground screw. Two wires, NO. Two fork terminals attached to to wires and attached to the ground screw - Yes.
Just twisted and one of the twisted wires attached to the ground screw - NO. That's where the greenee comes into play. the wirenit makes the gas tight connection and the hole passes one wire to the screw.

That twisted ground connection may not be making contact or making poor contact.


I'm going to get slightly technical and introduce this PDF: http://www.te.com/commerce/Document...BpdfEnglishENG_CD_10EB3_B.pdf1-6609020-0

If the right ground was not connected to ground, you would measure about 60V to that supposed ground terminal. Why? because the leakage path is about 0.21 mA. The capacitors are not ideal and have about the same leakage, so 1/2 of 120 V comes out of the wash.

So, that's one issue.

Your multimeter has a 10 meg input impedance so it acts like a 10 M resistor. It won't SEE that high impedance twist. There's little difference between 1000 ohms (for the twist) and 10 Meg ohms of the meter.

So suppose we have 20 feet if wire with two outlets daisy chained. Now make the ground not low impeadance at the first outlet. So, the first outlet say sees 10K to ground. The 120 V runs parallel and it can induce a voltage in the ground wire and possibly the neutral wire.
 

jorgeC

Joined Apr 20, 2012
1
Hi,
About induce a voltage in parallel wire it,s true, but to occurs this situation must flow a current on the hot wire. so i sugest to use a clamp to measure if realy exist current flow to the load.
Exuse my bad english.
 