Perhaps we can find some common ground here to agree on.
Let us suppose the efficiency is 80%.
Let us suppose the transformer is rated at 10V rms x 1A rms = 10W
Hence the power delivered to the load is 8W at 80% efficiency.
If the output voltage is 14V, the current = 8/14 = 0.57A
If we take two diode forward drop into account, the current = 8/12.6 = 0.63A
In either case, we derate the transformer from 1A rms to 0.6A DC.
This has nothing to do with the claim that 1A rms equals 1.4A peak.
It also agrees with the assumption that you can multiply rms voltage with rms current to give power rating.
According to the Hammond design guide, the DC voltage is derated from 10V to 9V.
The current is derated from 1A to 0.62A.
Power = 9V x 6.2A = 5.58W
That equates to an efficiency of 56%.
This was my original post #2 to the TS:
Let us suppose the efficiency is 80%.
Let us suppose the transformer is rated at 10V rms x 1A rms = 10W
Hence the power delivered to the load is 8W at 80% efficiency.
If the output voltage is 14V, the current = 8/14 = 0.57A
If we take two diode forward drop into account, the current = 8/12.6 = 0.63A
In either case, we derate the transformer from 1A rms to 0.6A DC.
This has nothing to do with the claim that 1A rms equals 1.4A peak.
It also agrees with the assumption that you can multiply rms voltage with rms current to give power rating.
According to the Hammond design guide, the DC voltage is derated from 10V to 9V.
The current is derated from 1A to 0.62A.
Power = 9V x 6.2A = 5.58W
That equates to an efficiency of 56%.
This was my original post #2 to the TS:
The TS wanted 3A output. What I had failed to identify was how much "more" the transformer has to be rated for. I stand corrected.For starters, put a bigger transformer, one that can deliver 3A and more.