Three phase 220v heating elements
madox
Joined May 9, 2019
5
Hi guys,
I've just bought a machine that works on three phase 220v. Can someone help me wire it to 220v single phase? I'm confused with the heating elements. How can I make them work on a single phase? Based in UK.
Attached electric diagram.
madox
Joined May 9, 2019
5
Hi casteels, hi Max,
Thank you for your replies.
First, want you to know I'm not an expert, but I'm trying to understand electricity.
The machine is rated 6.2 kW and it only has a small 0.2 kW motor controlled by the inverter. So each heating element should have 2 kW.
This parallel connection will be enough?
MaxHeadRoom
Joined Jul 18, 2013
30,695
I would make use of the contactor and the fuses for the 3 elements.
Also if you can use the existing internal conductors.
IOW, parallel up, up to the contactor input.
Max.
madox
Joined May 9, 2019
5
Max.
That's the best I can understand. Hope is right :)
I'll use L3 for heater N because is thicker and I think is better not to use the machine neutral wire.
Thank you for your time.
madox
Joined May 9, 2019
5
Hi guys,
It worked. The machine works great.
Thank you very much for your time.
Thanks Max. You are the best. :)