Thermal Differential Controller

Thread Starter

Ford Prefect

Joined Jun 14, 2010
245
Hi Guys,

I am curious. I am trying to design a thermal differential controller and ended up with the circuits as in the attached picture below.
If the temperature on the Collector thermister is greater (about 5⁰C degrees or more) than the temperature on the Storage thermister, then the pump runs, otherwise it is off.
Thermisters are rated as 5k @ 25⁰C degrees
Presets (VR1 and VR2-in both circuits) are 2k ohms
Pump (MT1) is rated as 12vDC 6W 0.5A

I wanted to ask your opinion, which would you consider is the better circuit - Circuit 1 or Circuit 2 and why?
And is there anything that I have not thought of?

Many thanks for your comments and thoughts.

PS. I may use an LM393 instead of an LM358

Differentail Controller.png
 
Last edited:

Kermit2

Joined Feb 5, 2010
4,162
My only suggestion is to flip the therms around electrically so they have one leg on ground instead of one leg on the positive battery bus.
 

crutschow

Joined Mar 14, 2008
34,432
I don't see any particular advantage of one circuit over the other, but the two pots in the first one could cause confusion in their adjustment.
Suggest you use one or two fixed resistors and one pot.
 

Thread Starter

Ford Prefect

Joined Jun 14, 2010
245
I vote for using the genuine comparator in this application. Not a big deal, just good form.
Yes, this is what I was also thinking, but, if I did use an LM358, then I can take out the pull up resistors - or do I need them?
If I use an LM393 then I would need the pull up resistors.
Agreed?
 

Kermit2

Joined Feb 5, 2010
4,162
If the sensors are remote mounted and must have wiring run to them. Keeping them ground referenced would simply mean no wire runs with a straight connection back to your 12 volt source.
Only a ground and signal wire. No worries if it is pinched, twisted, shorted, folded or mutilated.
Otherwise it is identical in function. :)
 

Thread Starter

Ford Prefect

Joined Jun 14, 2010
245
If the sensors are remote mounted and must have wiring run to them. Keeping them ground referenced would simply mean no wire runs with a straight connection back to your 12 volt source.
Only a ground and signal wire. No worries if it is pinched, twisted, shorted, folded or mutilated.
Otherwise it is identical in function.
:)
Yes, thank you, good point! :)
 