Shunt Capactive Compensation Load Power Factor

Thread Starter

jegues

Joined Sep 13, 2010
733
Did I do this correctly for the calculated quantities? Is this typical of what we would expect for a circuit like the following? Should the load angles be negative or positive?

The circuit is shown in pencil in the figure.

\(\vec{V_{s}} = 80 < 0^{o} V\)
 

Attachments

Last edited:

t_n_k

Joined Mar 6, 2009
5,455
Also - it might make more sense if the 300Ω load were placed in series with the various capacitive reactances, rather than in parallel.

In that case, when Xc=171Ω one would expect to reach the unity power factor condition.

The load (300Ω) voltage in that case would just be

80*300/(471) or 50.96 V @ 0°
 

Thread Starter

jegues

Joined Sep 13, 2010
733
I've attached a pdf of comments for your consideration.
Thank you very much for all the comments tnk, they are very helpfull, but as a result I've got a few more questions.

Particularly, as you don't provide the full details of the experiment other than the circuit sketch.
See the new figure attached to this post for the circuit, and all the details that we are given. (It's not much)

NOTE: When they show 300//j171 the complex part is supposed to represent the parallel capacitor, in other words,

\(300//-jX_{c}\)

Where in the table, the values for Xc are given.

You rightly show that the load voltage is 47.9 V @ -19.95° with no compensation so the current drawn
from the source (i.e. the total load current) is 0.16 A @ -19.95°. This corresponds to a load power factor

of cos(-19.95°)=0.94 lagging. But your table shows the power factor as unity.
Isn't the power factor the \(cos\theta\) where, \(\theta\) is the angle of the load in question.

I.e.

\(\theta = arg(\vec{Z}) = \frac{arg(\vec{V})}{arg(\vec{I})} = -19.95^{o} + 19.95^{o} = 0^{o} \)

Hence,

\(PF = cos\theta = 1\)

Am I doing something incorrect here?

I'm wondering in fact if the purely resistive 300Ω is always meant to be part of the load....???
I can assure you it is.

An obvious case of unity power factor for the total load would occur if Xc 171Ω replaced (not paralleled) the resistive 300Ω load. So the +j171Ω part of the 171+j171Ω block would be fully cancelled by a capacitive reactance of -j171Ω.
Correct, but we aren't allowed to change the orientation of the circuit. (i.e. must be paralleled)

Anymore comments/suggestions/concerns?

Everything you've mentioned so far has been helpful.
 

Attachments

t_n_k

Joined Mar 6, 2009
5,455
It's somewhat confusing that your hand drawn schematic sketch in the first post isn't the same as the schematic of figure L1-4. That's why I asked you to re-check the experimental schematic diagram.

As I look at the schematic in L1-4, I would interpret the load as being 300Ω||j171Ω. That is, a pure resistor of 300Ω in parallel with an inductive reactance of 171Ω ....??? I would also interpret the schematic to therefore include a parallel capacitive reactance of varying value - the point of the experiment.

You mention that

NOTE: When they show 300//j171 the complex part is supposed to represent the parallel capacitor, in other words,



This is even more confusing. How could +j171Ω be equivalent to -jXc?

You also didn't seem to address my question which asked if the goal of adding parallel capacitance was to improve load power factor then why don't your results show an improvement. Your results show a worsening load power factor as the parallel reactance decreases [equivalent to increasing capacitance]. If no parallel capacitance gives the optimum power factor [unity] then why add capacitance at all?

If the load starts out being just 300Ω with nothing else in parallel then one would expect the current and voltage in the load to be in phase - since it's purely resistive. So the load itself would have "unity power factor". To my way of thinking this isn't the conventional purpose of assigning a power factor. Power factor is usually applied to the source conditions. Where the source current and voltage are in phase then one regards this as a unity power factor condition.

Values using my assumption would be

Xc=1200, Load pf=0.554, mag_Vload=32.73V, arg_Vload=6.754deg

Xc=600, Load pf=0.623, mag_Vload=34.94V, arg_Vload=3.631deg

Xc=400, Load pf=0.706, mag_Vload=37.34V, arg_Vload=0.067deg

Xc=300, Load pf=0.798, mag_Vload=39.9V, arg_Vload=-4.004deg

Xc=200, Load pf=0.969, mag_Vload=45.28V, arg_Vload=-13.92deg

Xc=171, Load pf=1, mag_Vload=47.9V, arg_Vload=-19.95deg
 
Last edited: