That's why if you go contact type of sensor (clamping onto the actual gen mains) the stuff you put there has to accomodate 60Hz and 40Hz. Using a 60Hz rated device on 40Hz won't be good, but 50Hz is euro spec and easy to find, so device rated 50Hz will be ok on 60Hz supply and likely survive ok on 40Hz supply. You could also just clamp on a voltage divider (if the gen CT is tied to util CT/earth (I suspect it is), because I assume that's where the x-420 GND will be). Divide it down and bridge rectify it then clamp it with a regulator (use correct fusing). A step-down provides some isolation, which is a good thing.
The gen apparently has some measured voltage on it's mains while in exercise. You can use that to detect if it's running. Then add in a current sensor. If the gen has load then you know it's running and the xfer switch did it's job.
To know if say there was a util fail and the xfer switch failed, just use backend logic, like "yep, got alert for it's running, but no load sensed, and right now it's not exercise hour". There's no reason for the gen to run outside of exercise hour unless there was a util fail, etc.
It only needs two sensors to know all the states.
As a side note, contacless V detection is not hard, you can simply open one of these and accomodate it to sense V on gen mains. It has all the guts to act as a switch.
https://www.fluke.com/en-us/learn/blog/electrical/non-contact-voltage-detector-basics
The gen apparently has some measured voltage on it's mains while in exercise. You can use that to detect if it's running. Then add in a current sensor. If the gen has load then you know it's running and the xfer switch did it's job.
To know if say there was a util fail and the xfer switch failed, just use backend logic, like "yep, got alert for it's running, but no load sensed, and right now it's not exercise hour". There's no reason for the gen to run outside of exercise hour unless there was a util fail, etc.
It only needs two sensors to know all the states.
As a side note, contacless V detection is not hard, you can simply open one of these and accomodate it to sense V on gen mains. It has all the guts to act as a switch.
https://www.fluke.com/en-us/learn/blog/electrical/non-contact-voltage-detector-basics