Resistance in an AC relay
smellySamsquanch
Joined May 9, 2018
11
It has been a while since linear electric circuits and i think that my brain is missing some theory! I am looking up a mechanical relay's data sheet. Here are its specs:
120VAC operating coil voltage
3900 ohm coil impedance
Rated coil power of 1.35VA
https://www.mouser.com/datasheet/2/418/NG_DS_1308242_K10_0413-918463.pdf
I am unsure how the impedance calculates into the rated coil power. V^2/R does not compute... or my brain does not compute. I hook this relay right up to the mains supply and it operates properly, but wouldn't that be about 3.1A?
Any quick help would be appreciated!
38,632
You are confusing AC impedance with DC resistance (the coil DC resistance, not impedance, is 3900Ω).
Thus the coil AC current is 1.35VA/120V = 11.25mA.
The coil impedance (due to the vector sum of the coil inductive reactance and resistance) is then 120V/11.25mA = 10.7kΩ (nearly 3 times the DC resistance).
smellySamsquanch
Joined May 9, 2018
11
Ok, thanks for the help! I need to focus more on its inductance then?
MaxHeadRoom
Joined Jul 18, 2013
30,766
The specs for the AC versions can be misleading, you are better off to go with the rated coil power value.
Compare it to the DC version for 110vdc!
Max.
smellySamsquanch
Joined May 9, 2018
11
You need to include the inductance, as the coil's inductive reactance is the majority of the coil AC impedance.
Are you familiar with inductive reactance and AC impedance calculations?
It has been a little while since i've gone thru the paces (and i never used it afterwards). I am very interested if you would like to throw some knowledge at me. I will try to follow along. Ive been digging around in my notes but am still confused. Is there a formula you could point me to? I noticed the reactance is the derivative of current W/R/T Time? I also suppose it transfers into the phasor realm somehow. but that's all i can remember at the moment.
Thanks.
P.S. This is just one of those things I stumble across while working that doesn't really impact my ability to finish the project, but not knowing the correct answer is killing me!
thespackler
Joined Apr 20, 2018
You're dealing with reactive power here because it's AC. And because it's a coil the total impedance will be primarily inductive reactance and a bit of ohmic resistance from the coil itself. The formula for inductive reactance is XL = 2πfL where f is the frequency (60 Hz in your case) and L is the inductance of the coil, which you may find on the data sheet. Here's an article that gives some more detail on AC power and reactance: https://circuitcrush.com/electric-power-primer-2/
smellySamsquanch
Joined May 9, 2018
11
Thanks everybody for your assistance! Very knowledgeable group!
I am just going to sum up things below so if anybody reads this they can get straight to it.
Problem: Making my tiny brain understand how the given values on a relay's datasheet relate to one another.
Given:
120VAC @ 60Hz (possibly need to change this to Vrms = 84.9Vrms Ill let someone else chime on this)
Coil Resistance = 3900 ohms
Rated Coil Power = 1.35 VA (I am thinking this is derived with Irms and Vrms since it is VA, but again someone else should chime)
Formulas to Derive More Info:
Current = V/I = 1.35VA/120VAC = .011A
Total Impedance = Z = V/I = 120VAC/.01125A = 1.07E4 Ohms
Reactance = Xl = Sqrt(Z^2 - R^2) = Sqrt(10666.7^2 - 3900^2) = 9.93E3 Ohms
If : Xl = 2pifL
Inductance = L = Xl/(2pif) = 9928.13063/(2*pi*60Hz) = 26.3H
Notes:
I was mistakenly treating the relay's coil as pure resistance. It needs to be calculated as a resistive and inductive series circuit. I am still confused as to if i should be using the rms voltage and current. That would seem more propper. I would also like to be able to wrap it all back together in full circle of equations. I am thinking power was supposed to be P=Vrms*Irms*cos(60). This does not wrap back around with their supplied values however. May just be coincidence, but when you calculate 120/coil resistance, it is dangerously close to the above power calc.
MaxHeadRoom
Joined Jul 18, 2013
30,766
The simplest away around it is to use DC coil relays! :)
Apart from the instant at switch on, the DC are the more efficient and less likely to fail if the armature does not seal completely.
A simple bridge is all that is needed for a supply.
Max.
smellySamsquanch
Joined May 9, 2018
11
Max.
Agreed! This is just what i had lying around.
jeff
38,632
No.
120Vac is RMS already, not peak voltage.
Where did you get 60?
That should be the phase angle between voltage and current, not frequency.
A simple way to calculate the coil power here is I²R, where I is the current and R is the coil resistance.
Thus, the (real) relay power used would be 0.011² * 3900 = 0.472W.