Rectifier for 220 AC to DC to supply solenoid valve

Thread Starter

Gurumurthi

Joined May 3, 2019
3
I have a solenoid valve in a Crane’s hydraulic system to be tested. Specs of solenoid valve mentioned as 220V, 60 Hz.
Solenoid valve didn’t energise when 220, 50 Hz AC supply given.
Understood from maker that a rectifier is incorporated in the Din connector and final supply to the Solenoid coil required is “DC”.
Rectifier not available to test the valve. The resistance of solenoid coil mentioned as “150 ohms”, measured & found correct.
Tried with Bridge rectifier, blowing out repeatedly.
Can any one help me with solution reg correct specs for the rectifier to be used.
 

Thread Starter

Gurumurthi

Joined May 3, 2019
3
I have a solenoid valve in a Crane’s hydraulic system to be tested. Specs of solenoid valve mentioned as 220V, 60 Hz.
Solenoid valve didn’t energise when 220, 50 Hz AC supply given.
Understood from maker that a rectifier is incorporated in the Din connector and final supply to the Solenoid coil required is “DC”.
Rectifier not available to test the valve. The resistance of solenoid coil mentioned as “150 ohms”, measured & found correct.
Tried with Bridge rectifier, blowing out repeatedly.
Can any one help me with solution reg correct specs for the rectifier to be used.
A correction(typho error) -solenoid coil resistance is 1500 ohms.(not 150 ohms).
 

crutschow

Joined Mar 14, 2008
38,689
With 1500 ohms the current with 220V full-wave rectified voltage should be less that 0.2A RMS.

What was the voltage and current rating of the bridge you used?
It should be a least 400V and 0.5A.
 

Thread Starter

Gurumurthi

Joined May 3, 2019
3
With 1500 ohms the current with 220V full-wave rectified voltage should be less that 0.2A RMS.

What was the voltage and current rating of the bridge you used?
It should be a least 400V and 0.5A.
Many thanks Mr.Crutschow,
The rectifier used was 700 v ac(RMS) and 2.0 Amps, but there was some short circuit in the wiring, now eliminated and working fine.
 