PT100 resistance into voltage ?
khalad
Joined Feb 9, 2017
55
Linearisation is likely done in the transmitter.
There are two calibration scews (potentiometers) on the transmitter.
The following picture shows wich screw has the function of offset (o) and gain:
You will need two known temperatures to calibrate.
Usualy melting ice (0 °C) and boiling water (100 °C) are used.
so how the equation will look like to find the temperature if i am using 100ohm
bertus
Joined Apr 5, 2008
22,930
What is the input range of the used ADC?
The formula depends on which ADC values you will see at 0.4 Volts and 2 Volts.
khalad
Joined Feb 9, 2017
55
void setup() {
// put your setup code here, to run once:
pinMode(A0,INPUT);
Serial.begin(9600);
float prev = 17;
void loop() {
// put your main code here, to run repeatedly:
float v=analogRead(A0);
float V=v/1024.5*5.0;
float T=-50+(V-0.4)*(150+50)/(2-0.4);
float T_new = 0.75*prev + 0.25*T;
prev = T_new;
Serial.println(T_new);
delay(100);
bertus
Joined Apr 5, 2008
22,930
As I asked, what is the range of the used ADC?
If you only use 2 volts range on a 5 Volts ADC, you will loose resolution.
When you use a 250 Ohms resistor, the transmitter will put out between 1 and 5 Volts.
The 250 Ohms can easily be made with 4 1K resistors in parallel.
khalad
Joined Feb 9, 2017
55
i supply the transmitter with 24v
bertus
Joined Apr 5, 2008
22,930
But the transmitter puts out current from 4 to 20 mA.
When you use a resistor of 100 Ohms that will give you a voltage range of 0.4 to 2 Volts.
With a 250 Ohms resitor the voltage raneg will be from 1 to 5 Volts.