As a beginner to this topic, you've wonderfully explained the working of the PID technology in a very good concise way.I can give you a quick introduction to PID control.
P = proportional
I = integral
D = derivative
You can make a controller with P alone, PI, PD, or PID.
Let us use a temperature controller for an oven as an example.
Ttarget is the temperature you wish to attain.
T is the present measured temperature
Terror = Ttarget - T
In a controller, the goal is to bring Terror to zero as quickly and smoothly as possible.
For this we need to develop three parameters or multipliers (i.e. gain):
Kp
Ki
Kd
P controller
V = Kp x Terror
where V represents the voltage (or controlling parameter) applied to the system to reach the target.
Here we can see that we need to increase the voltage when the error is large. We reduce the voltage to zero when the target is reached.
PI controller
V = Kp x Terror + Ki x sum(Terror)
In the P controller, we can imagine that when the target temperature is attained, the temperature will tend to drift away if the controller voltage V is set to zero. We need to maintain a steady voltage to maintain the status quo. That is where the integral term comes into play.
What is the integral?
The integral is the summation over time of repeated error measurements. When we are far away from the target the error is large. When we have reached the target the error will oscillate about zero. Over time the integral will settle to a finite value that represents this DC offset that needs to be applied to the controlling voltage.
PID controller
V = Kp x Terror + Ki x sum(Terror) + Kd x rate_of_change(Terror)
The derivative term introduces the rate of change of the error.
Rate of change is measured as ΔTerror/Δtime
Imagine that this is a heated oven and someone opens the door of the oven.
The temperature falls suddenly. The rate of change is a measurement of how quickly the temperature changed over a given time, for example, 5 seconds.
The derivative term allows the controller to make quick corrections due to perturbations, i.e. rapidly changing conditions.
So that is a PID controller in a nutshell.
Tuning a PID controller involves performing various tests or via trial and error in order to determine the appropriate values for Kp, Ki, and Kd.
Edit:
If your K values are too low, the system will be slow to reach the target or may never reach the target.
If your K values are too high, the system will overshoot the target and may oscillate about the target.
Choosing the right values of K will allow the system to reach the target as quickly as possible and not overshoot or oscillate.
Quite awesome, l like your explanation which gives me a clear understanding of how it works. Years ago, l've come up on a
website that was as similar in terms of a good simplistic view.
Moderator edit: New thread created from this.