Thanks for answerI don't see any problem using a busbar, but why the reason and not flexible copper conductor?
One more question, It is also good idea to put 3x20mm2 busbar inside 1" PVC pipe, inner diameter is 30mm with 1mm thickness, it is can decrease or increase capacity ?, especially short circuit (kA) capacity ?Thanks for answer
Because busbar is more cheap in my area
Example, 50mm2 is equivalent with 3x20mm busbar in price, but 3x20mm busbar have less resistance and bigger capacity
Also for prevent copper thief, I think to cut busbar is hard than cut wire
Short circuit capacity is expected more than 50kA for properly absorbs lightningOne more question, It is also good idea to put 3x20mm2 busbar inside 1" PVC pipe, inner diameter is 30mm with 1mm thickness, it is can decrease or increase capacity ?, especially short circuit (kA) capacity ?
Normal earth GND and also lightning down conductorSo this is also intended for lightning conductor or normal earth GND conductor.?