as @MaxHeadRoom says...Not really significantly.
What's if we use NH fuse ? It is more instantly cut the circuit ?Under a short condition, a larger wire will have less resistance and conduct more current, so probably the breaker will trip faster.
Another way to think about it. (not a short condition)
1)10A breaker. 10.1A load, 16A wire, voltage loss because of the wire is 10 volts, the breaker pops in 5 minutes.
2)10A breaker, 35A wire so the loss in the wire will be less so lets say there is 5 volts loss in the wire, so the voltage on the load is higher by 5 volts than in example (1), so the load is 10.6A. Now the breaker will pop in 2 minutes.
3) 10000A wire, wire loss is almost nothing, voltage on the load is higher, current is 11.1A and the breaker pops in 30 seconds.
I think circuit breaker specifically MCB is not really safe...Under a short condition, a larger wire will have less resistance and conduct more current, so probably the breaker will trip faster.
Another way to think about it. (not a short condition)
1)10A breaker. 10.1A load, 16A wire, voltage loss because of the wire is 10 volts, the breaker pops in 5 minutes.
2)10A breaker, 35A wire so the loss in the wire will be less so lets say there is 5 volts loss in the wire, so the voltage on the load is higher by 5 volts than in example (1), so the load is 10.6A. Now the breaker will pop in 2 minutes.
3) 10000A wire, wire loss is almost nothing, voltage on the load is higher, current is 11.1A and the breaker pops in 30 seconds.
Safe for what, human interaction or circuit protection.I think circuit breaker specifically MCB is not really safe...
It is copper not aluminium, aluminium is so bad, also difficult to find in my local area, minimum size is 10mm², and it's very large for office use, imagine you have 3x10mm² aluminium XLPE insulated wire under the table, also aluminium outlets it's hard to findA proper circuit breaker has a defined overload versus time characteristic and so the wire size, as long as it is at least adequate, will not have an effect worth considering. So using 20 amp wire on a circuit with a 15 amp breaker provides no benefit, except if there is a need to change to a 20 amp breaker in the future.
Of course, this is assuming that copper wire is used.
With aluminum wire there may be some benefit in using 30 amp wire for a 10 amp circuit, if the proper connection arrangements are used. That mmay tend to reduce the wire heating somewhat.
Yes... it's good idea to install CT sensor with micro-controller and detect when something is shorted then trip a contactor coil / mccb with shunt trip ?Only if the breaker was intelligent enough to know what size wire you had. It only uses what's inside to make it's determination
Circuit protection, not human interraction, for example it outlet contact made from thin copper is burnt, or shorted that MCB can't cut power so instantlySafe for what, human interaction or circuit protection.
No... I just wan to make installation with can properly used even degraded by age, so... I calculate maximum use of wire is about ~30%, if 10 years later capacity is degraded 15% that wire still only use ~38% capacity, it's very safeA proper circuit breaker has a defined overload versus time characteristic and so the wire size, as long as it is at least adequate, will not have an effect worth considering. So using 20 amp wire on a circuit with a 15 amp breaker provides no benefit, except if there is a need to change to a 20 amp breaker in the future.
Of course, this is assuming that copper wire is used.
With aluminum wire there may be some benefit in using 30 amp wire for a 10 amp circuit, if the proper connection arrangements are used. That mmay tend to reduce the wire heating somewhat.
Ok... it is good idea for use aluminum wire for outdoor purpose ?, wind turbine ? generator set ?My point in mentioning aluminum wire is that it has a number of different additional challenges. I do not ever recommend aluminum wire, nor components, for interior power wiring.
OUr utility companies use aluminum wire for distribution. It reaches as far as my house, where it transitions to the copper wire that I provided. I do not choose to use aluminum wire at all, anywhere. It is much more effort to make a good connection with it and so I do not recommend it anywhere.Ok... it is good idea for use aluminum wire for outdoor purpose ?, wind turbine ? generator set ?