For a offgrid solar powered house with 48v battery, I've tested the FCHAO 3500w-48 inverter for a bit, and it seems to be the best option I can find in terms of idle consumption.
However, the ground on this thing is a quite powerful 12-30Vac voltage compared to battery negative.
This is causing issues with other components that has their chassis connected to the negative DC terminal. All of a sudden I have two different ground potentials that has 0Vdc between them, but upto 30Vac between them. And to make matters even worse, the inverter is only 3500w, so I need two of them. If they happen to power on so that their frequencies becomes opposite of each other, I get 3 ground potentials with up to 60Vac between them.
If they are mounted in the same metal cabinet, disaster is guaranteed.
How should I deal with this?
The unit itself is aluminum, connected to the PCB ground through a bunch of screws. The metal is covered in an isolated paint that makes it safe to touch, except for the screws. The problem is however, what to do with the mounting screws and outlet ground connections? I don't want three different ground potentials in the house - suddenly there is a risk of fire if ground touches ground!
The ground voltage (compared to battery negative) is steady 12.9Vac at idle, increasing by about 1Vac for every 200W of load connected.
The solution that comes to my mind is to connect the outlets ground internally to battery negative rather than inverter chassis. Then create some isolation mounts so that inverter chassis never gets in contact with the cabinet it's mounted into. Does this introduce some issues I have not realized yet?
(For all inverters I've used before this, the inverter ground has been floating relative to the battery negative, so connecting them together has been a solution to make a common ground.)
However, the ground on this thing is a quite powerful 12-30Vac voltage compared to battery negative.
This is causing issues with other components that has their chassis connected to the negative DC terminal. All of a sudden I have two different ground potentials that has 0Vdc between them, but upto 30Vac between them. And to make matters even worse, the inverter is only 3500w, so I need two of them. If they happen to power on so that their frequencies becomes opposite of each other, I get 3 ground potentials with up to 60Vac between them.
If they are mounted in the same metal cabinet, disaster is guaranteed.
How should I deal with this?
The unit itself is aluminum, connected to the PCB ground through a bunch of screws. The metal is covered in an isolated paint that makes it safe to touch, except for the screws. The problem is however, what to do with the mounting screws and outlet ground connections? I don't want three different ground potentials in the house - suddenly there is a risk of fire if ground touches ground!
The ground voltage (compared to battery negative) is steady 12.9Vac at idle, increasing by about 1Vac for every 200W of load connected.
The solution that comes to my mind is to connect the outlets ground internally to battery negative rather than inverter chassis. Then create some isolation mounts so that inverter chassis never gets in contact with the cabinet it's mounted into. Does this introduce some issues I have not realized yet?
(For all inverters I've used before this, the inverter ground has been floating relative to the battery negative, so connecting them together has been a solution to make a common ground.)