Tied per NEC. Any one pole might be tripping. Amp-clamp each line to see if there's one that is way more than the others.Here is a pic of the acutal breaker in place as well.View attachment 258202
That nameplate says it's a STEP DOWN transformer.Here is a pic of the transformer. Last time I attempted to turn on the circuit breaker, I literally turned off every other breaker in the panel. View attachment 258203
I suspect the issue is just energizing the xfrmr. If it could energize, it's 2.3x more amps (+ some extra for efficiency loss) to go 208 to 480, a 50A load on 480 will easily blow 100A fuses on the primary side.If the MAIN'S are 100 amp and you're switching a 100 amp load - any other circuitry that might be drawing current will easily put the fuse over limit and blow it. Breakers tolerate higher startup current to a degree. A sustained 100 amp draw shouldn't blow a breaker but it might blow a fuse.
Not sure if they need to be spec'd per NEC OCPD for motor, those breakers are not branch ckt breakers, they don't feed motors. They likely are feeder breakers.A set of #1-gauge Wires are rated for 150-Amps, (unless they run for more than ~100-feet),
but the Main-Disconnect-Switch will have to be changed-out for a 200-Amp Model.
You didn't state the rated capacity of your Circuit-Breaker-Panel, it may already be a 200-Amp Model.
It would be a bonus to replace it with a "Main-Breaker" style Panel and eliminate all those Fuses.
Also, the 3-Pole Circuit-Breaker that You provided a picture of,
may not be rated for "Motor-Duty", (there's a proper acronym for it but it's been ~30-years).
There are Breakers specifically designed with a Delayed-Trip-Time for Motor-Loads.
I think OP needs to go back and see if that step down can be used a a step up.the fast acting fuses wont suffice, you'll need an RK5 type fuse.
Step-down transformers may be
reverse fed for step-up operation to
increase voltage. This means that
the incoming power is connected to
the low voltage (X’s) and the load
is connected to the high voltage
(H’s). If the low voltage is wye,
the X0 terminal must NOT be connected
in any way. Likewise, if the
low voltage is a delta with a 120
volt lighting tap (high-leg), the X4
terminal must NOT be connected
in any way.
CAUTION: Much higher than
normal inrush currents may occur
with reverse feed operation and
may cause nuisance fuse blowing
or breaker tripping. For this reason,
fuses and breakers with time-delay
characteristics must be used.
If a breaker is used for incoming
over-current protection, it must be a
thermal-magnetic type breaker, not
a magnetic-only type breaker.
typically they can be used up or down. A clamp will not give you a meaningful measurement.I think OP needs to go back and see if that step down can be used a a step up.
If ok, change fuse types.
Amp-clamp the line(s) to get an idea of actual inrush. All three to make sure there's no weird imbalance.
If I clamp a line and set my clamp on inrush, why would it not give me a accurate reading of the amps on the clamped line?typically they can be used up or down. A clamp will not give you a meaningful measurement.
Ok, if your meter has that function, you'll have a reading.If I clamp a line and set my clamp on inrush, why would it not give me a accurate reading of the amps on the clamped line?
Another Q I have is, should energize amps be pulling ~100A+ inrush on all three lines, or even that much on any input line?
can you draw a single line schematic from service infeed to load.No breakers on the 480v side, just a 60 amp disconnect switch before the waterjet. So the RK5 fuse looks like a bigger fuse than what's allowable in the disconnect I have at the main. Is it possible that BOLTSWITCH makes an RK5 type fuse holder or how would I go about that??
No OCPD on the 480v3ph branch ckt? Isnt that a violation of NEC? The disco is a non-fuse type?No breakers on the 480v side, just a 60 amp disconnect switch before the waterjet. So the RK5 fuse looks like a bigger fuse than what's allowable in the disconnect I have at the main. Is it possible that BOLTSWITCH makes an RK5 type fuse holder or how would I go about that??
Are there any other circuits coming off of the service disconnect, or does it run directly to the the panel board?I may have worded it incorreclty. there is a 60 amp fused safety switch between the waterjet and transformer. Here is crude drawing of the layout.
| Thread starter | Similar threads | Forum | Replies | Date |
|---|---|---|---|---|
|
|
Inrush current limit using NTC | Power Electronics | 19 | |
|
|
USB inrush current limiter | Power Electronics | 6 | |
| E | Inrush Current Measurement | Test & Measurement | 5 | |
|
|
Inrush current imact on Circuit breakers upstream of motor | General Electronics Chat | 9 | |
| T | Issue with inrush current circuit | Power Electronics | 7 |