how many strands in 0.75mm2 cable for ducting

Thread Starter

thor21

Joined Sep 29, 2024
421
hello, i need to install 4 core 0.75mm cable into wall and put it into the duct

there is an option to buy 0.75mm2 cable with 7 or 20 strands. any idea which fits better? thanks!

1760951235705.png
 

MrChips

Joined Oct 2, 2009
34,626
20 strands would be a more flexible cable.

Sounds like 18 AWG cable. The bottom line is can you fit the required number of cables in the conduit? Can the cables carry the required current?
 

Thread Starter

thor21

Joined Sep 29, 2024
421
@MrChips so more strands more flexible and better for ducts?

yes its 18 AWG, and i already calculated the required current which is 2A. I will have to have one big duct or 2x smaller ducts. not sure whats better.

thanks
 

MrChips

Joined Oct 2, 2009
34,626
A more flexible cable would be easier to pull through a duct.
You need to determine the length of the cable and calculate the resistance, voltage loss, power dissipation, and temperature rise.
 

Thread Starter

thor21

Joined Sep 29, 2024
421
You need to determine the length of the cable and calculate the resistance, voltage loss, power dissipation, and temperature rise.
what do u mean by
1) resistance
2) i did that - got around 0.5V on of cable length 7m
3) whats power dissipation?
4) by temp rise you mean? If the endpoint device is DC 5V/3A max.


thanks
 

Ian0

Joined Aug 7, 2020
13,097
Conduit cable is available in all sizes and nearly always has 7 strands. Tri-rated cable tends to have 0.2mm 0.25mm or 0.3mm strands and many more of them. Both have the same resistance, voltage drop and temperature rise at DC, 50Hz or 60Hz. 7 strand will be flexible enough. Either will go down smooth conduit, however for flexible conduit I would recommend the 7 strand as it is not too flexible. The 24*0.2mm trirated cable will tend to get caught on the ridges as you push it down flexible conduit. If you are dragging it through, then either type is equally as good.
 

Thread Starter

thor21

Joined Sep 29, 2024
421
@Ian0
thanks

so conduit cable is for a specific purpose? compare to Trirated cable? Is it possible to say purpose for conduit and trirated?

By graggig it through i need some tool? thanks
 

MrChips

Joined Oct 2, 2009
34,626
It is easier to pull cables than push cables.

Tie a heavy bolt or nut to the end of a string and drop it through the full length of the conduit. Tie all the required cables to the string and pull the cables through.
 

panic mode

Joined Oct 10, 2011
4,864
there is an option to buy 0.75mm2 cable with 7 or 20 strands. any idea which fits better? thanks!
that depends on application... which is why there are different options - from solid wire to one with many fine strands.
solid wire is suitable for applications with no movement. and the more movement there is, the finer strands are needed. 0.75mm2 wire with 7 or 20 strands would not last long in a robotic application.
 

Ian0

Joined Aug 7, 2020
13,097
@Ian0
thanks

so conduit cable is for a specific purpose? compare to Trirated cable? Is it possible to say purpose for conduit and trirated?

By graggig it through i need some tool? thanks
Conduit wire is for conduits, Trirated is for anything else that needs a single wire insulated to mains voltage standard. Nothing to say that you can’t use trirated in conduit, but the 7 stranded stuff is good inside a conduit it doesn’t get flexed.
https://www.drapertools.com/product/56761/electricians-draw-tape-in-plastic-case-15m/
unless you have the option of hanging it vertically and dropping a weight through it as @MrChips suggested.

I ran some CAT5 in flexible conduit under the lawn and around a flower-bed by a circuitous route to get to the microwave antenna for the internet. With the usual flexible CAT5 it was a complete pain to do, it just kept getting stuck in the grooves in the conduit. Using the stiffer outdoor CAT5 it was much easier.
 

Thread Starter

thor21

Joined Sep 29, 2024
421
flexible CAT5 it was a complete pain to do, it just kept getting stuck in the grooves in the conduit. Using the stiffer outdoor CAT5 it was much easier.
@Ian0
which implies the stiffer less strands - easier to go thru the conduit? chagpt said opposite :(
 

Ian0

Joined Aug 7, 2020
13,097
@Ian0
which implies the stiffer less strands - easier to go thru the conduit? chagpt said opposite :(
How many times has ChatGPT run wires through conduit?
it needs to be just flexible enough.Like 1/0.8mm might be a bit too stiff. Obviously, it’s better if you can pull it through rather than push, if you are going to pull it then first you need something in there to pull it with.
You might find that LSZH on 24/0.2 is better than PVC because the insulation is slightly stiffer, but from a smoke point of view LSZH is PVC conduit is a bit silly!
 
Last edited:

panic mode

Joined Oct 10, 2011
4,864
@panic mode my application is to install it into the conduit, one end pane, other end PSU. that's it.
is the conduit going to move or flex after installation? is it part of the system that bends every few seconds due to some actuator? if so you may want to consider of suitable size and carefully consider bending diameter based on cable rating:
1760975982478.png


as far as electrical code is concerned, all conductors should be solid. but for practical reasons this is often not the case so only ends may be "solid" (by crimping etc.).

since you are placing this into the wall of a home, this is not moving at all. even solid wires are fine (just look at your existing house wiring).

LSZH is "low smoke zero halogen" and PVC is rather "smoky". Ian0 was just saying that it does combination does not make much sense.
 
Last edited:

drjohsmith

Joined Dec 13, 2021
1,548
Yes , 7 or 20 strand cable, or just about any other is fine to put in conduit

The chatter above is valid , but more for debate.
all this is said, but:

the more the number of strands of cable for a given overall size, the more flexible the cable will be,
if you took a spoon, and kept bending it , it would break, if our spoon as made of 100 strands, it would be not much use as a spoon, but it would be very hard to break by bending !
so if conduit is fixed, any cable is fine, if its just occasionally moved , say to get behind the machine occasionally, then any apart from the single / solid core is fine, if conduit is constantly moving, a more flexible say 20 strand would be if use.

The comments about power / voltage drop are to do with heating,
all none super conductor cables have a resistance, and get "warm" ,
If you tightly pack a condit with cables, and put that conduit in an insulated environment, classic is under insulation in the attic, the cables cna get very warm / burn. From the numbers you have shared this should not be a problem, as your conduit is not packed, and your only puting a limited current down the cable, well within the capabilities of the cable. Just check you have a fuse, so under fault conditions you dont draw a much higher current.
 
Last edited:

Ian0

Joined Aug 7, 2020
13,097
what does that mean?

Okay - so is it still okay to run 20strands/0.75mm2 thru conduit? Or should i buy 7strands/0.75mm2?
Low Smoke Zero Halogen.
You can run whatever you like through conduit. The conduit serves only to protect the wiring from damage as per section 522 of the IEE Wiring Regulations
 

Thread Starter

thor21

Joined Sep 29, 2024
421
just one more note ... ist it better to use
2x 0.75mm2 rated for 50V (they claim its speakers?/ generic <50V cable)
(but they dont state) how many Ampers can sustain.

The price of two of these is still half of the one below, maybe two of these occupy also less space as one 4 core?
1761074861113.png

instead of
4x0.75 mm ; this is rated for 300/500V; 15A
1761074881492.png
 
Last edited:

drjohsmith

Joined Dec 13, 2021
1,548
just one more note ... ist it better to use
2x 0.75mm2 rated for 50V
(but they dont state) A.
The price of two of these is still half of the one below.
View attachment 357438

instead of
4x0.75 mm ; this is rated for 300/500V; 15A
View attachment 357439
easier to use ?
if you use two cables the same you have to put cables on them , still risk getting it wrong .

so to me easier is the 4 wire cable, but nite that's the three phase mains cable colours, so might be confusing.

personaly, id be using 4 separate cables , of different colours .


Just a note, remember to include in your costs your time to decide and impliment .
 

Ian0

Joined Aug 7, 2020
13,097
just one more note ... ist it better to use
2x 0.75mm2 rated for 50V
(but they dont state) A.
The price of two of these is still half of the one below.
View attachment 357438

instead of
4x0.75 mm ; this is rated for 300/500V; 15A
View attachment 357439
For <50V you can use 50V rated cable. For mains, it must be double insulated. And 0.75mm is rated at 6A (not 15A). It can be uprated to 10A for an appliance cord of <2m length.
 