Suppose you have 120v going to a load. How come when you measure from hot to chassis, you get 60v? Half. I never quite understood this.
It sounds to me like you have something running off of a "centre tapped transformer". Here in the UK, these are used extensively on building sites to power tools.Suppose you have 120v going to a load. How come when you measure from hot to chassis, you get 60v? Half. I never quite understood this.
Sounds like a serious problem to me. The chassis should be connected to the ground wire and be electrically isolated from the hot line. In the US, chassis ground should also be isolated from neutral. The only place ground and neutral are supposed to be connected is in the circuit breaker box.Suppose you have 120v going to a load. How come when you measure from hot to chassis, you get 60v? Half. I never quite understood this.
If the voltage is real, even a 10k resistor would draw enough current to heat up quickly, wouldn't it? I come up with 360mW, unless I just did the math wrong.Add a 10kΩ resistor between hot and chassis and see if the voltage changes.
The reason for a test such as this is to see if it sustains the current, IOW, does the voltage collapse when a lower impedance path is offered?If the voltage is real, even a 10k resistor would draw enough current to heat up quickly, wouldn't it? I come up with 360mW, unless I just did the math wrong.
Right, but if not, you better be using a fat resistor, or else you won't want to leave it turned on very long!The reason for a test such as this is to see if it sustains the current, IOW, does the voltage collapse when a lower impedance path is offered?
If so, it suggests a reading due to the high impedance meter, possibly from the inductive or capacitive means.
Max.
Under this condition, you would find the other half from neutral to chassis!Suppose you have 120v going to a load. How come when you measure from hot to chassis, you get 60v? Half. I never quite understood this.