Help with wiring diagram(temperature sensor and temperature controller)
krumplicukor
Joined Aug 6, 2018
8
I am trying to create a small project which consist of:
-PT100 temperature sensor (2 wires)
-heating mat(2 wires)
-a solid state relay
-a temperature controller
I am struggling with creating a wiring diagram
I would really appreciate if someone could help me :)
MOD:Rotated your image.E
bertus
Joined Apr 5, 2008
22,998
It is not clear waht the supply voltage of the controller is.
For connecting the SSR connect 3 from the controller to 3 of the SSR and 4 of the controller to 4 of the SSR.
For the PT100 short 10 with 11 and connect the PT100 to 11 and 12.
Bertus
krumplicukor
Joined Aug 6, 2018
8
Bertus
Thank you so much, the supply is 240V
38,748
The SSR needs a 3-32Vdc control input voltage.
That can be obtained from a 5Vdc wallwort in series with controller pin 3 (minus) and pin +3 (plus) of the SSR.
Reloadron
Joined Jan 15, 2015
7,922
You may want to look in detail at the controller you have there. Sometimes a controller, based on part number and options may have dry contact outputs or an SSR output. Got a part number for your controller? The picture seems to reflect dry contacts and also a SSR output. Much like the unit reflects using different inputs. Sometimes the Inputs/Outputs are user configurable and sometimes they are factory set. The data sheet or manual for your controller should cover that and the configurations.
Ron
28,145
For the question about the SSR, certainly the literature that comes with the controller must be consulted, since it is not likely to be both at the same time.