help needed with ups

Discussion in 'Power Electronics' started by paachu802, Dec 29, 2016.

  1. paachu802

    Thread Starter New Member

    Feb 5, 2014
    29
    2
    I want to connect ups in my home this is my home connection..for simplicity i havenot shown fuse,main switch,and earthing....from RCCB phase is distributed to MCB's and from MCB's to Switchboxes which have one socket and switches for lights and fans.... Neutral is directly connected to boxes to lights and fans..Motor is directly connected without MCB through one switch(not shown in fig) Untitled.png this is fig2 ...i supposed to connect plz help ...i have opened connection at RCCB output to the iput of ups through a socket in Box 3 and output of UPS is fedback through box3 socket no.2 to its MCB ...is it ok Untitled2.png
     
  2. Kermit2

    AAC Fanatic!

    Feb 5, 2010
    4,158
    1,125
    You need neutral line to UPS

    Your UPS output is going to the output side of the breaker.

    You have no disconnect between your UPS system and utilities. You must disconnect utilities from your system when using the UPS.
     
  3. paachu802

    Thread Starter New Member

    Feb 5, 2014
    29
    2
    thanks for reply..Kermit2..i was not feeling well past weeks sorry for late comments....i will connect netral from ups..i want to know is my connection ok...and i want to know at which part the rest of circuit is isolated when main power fails...is it inside ups or RCCB does not conduct in reverse direction??????
     