Hello all!
Have come across a problem which i thought would be solved with the RC snubber but alas not. Starting to now question my own understanding of the situation so hopefully someone could set me straight.
The set up is a simple gate panel which has no dry contacts. I need at least one so that i can detect when the gate is open/closed and send that to our home automation system. Trouble is, the only method of getting an output signal from the gate's PLC is to use a pair of 24vac contacts (normally used for a flashing yellow warning light that is mounted to the gate). No problem there, so i wired up a simple AC relay like this which gives me a pair of volt-free contacts to use. The other side of the relay is then connected to the automation device with a contact-pair that loops 12v DC down it to detect when the gate is open. If the gate is actuated, 24vac is then sent to the coil/relay which closes the NO contact and loops the 12v dc back to the automation system. Simples...right?
No. The problem i immediately found what that after a short while, it appears the PLC crashes and i assumed this was because i forgot to add a snubber across the coil. So, soldered a 470ohm resistor to a 0.1μF cap and wired them across the terminals on the coil side. It immediately tripped the panel and blew the 1a fuse providing power to the acessories.
Am i making the mistake that it's not actually the 24vac i need to worry about (since the frequency is too quick for the coil to build enough inductance) but it's the 12v DC side that is causing the panel to eventually crash requiring a reset? Should i be placing the snubber network on the contact side then as a result?
Been at this for a few days and i'm trying to avoid running over to ChatGPT and further its plans for world domination.
Thanks
pops
Have come across a problem which i thought would be solved with the RC snubber but alas not. Starting to now question my own understanding of the situation so hopefully someone could set me straight.
The set up is a simple gate panel which has no dry contacts. I need at least one so that i can detect when the gate is open/closed and send that to our home automation system. Trouble is, the only method of getting an output signal from the gate's PLC is to use a pair of 24vac contacts (normally used for a flashing yellow warning light that is mounted to the gate). No problem there, so i wired up a simple AC relay like this which gives me a pair of volt-free contacts to use. The other side of the relay is then connected to the automation device with a contact-pair that loops 12v DC down it to detect when the gate is open. If the gate is actuated, 24vac is then sent to the coil/relay which closes the NO contact and loops the 12v dc back to the automation system. Simples...right?
No. The problem i immediately found what that after a short while, it appears the PLC crashes and i assumed this was because i forgot to add a snubber across the coil. So, soldered a 470ohm resistor to a 0.1μF cap and wired them across the terminals on the coil side. It immediately tripped the panel and blew the 1a fuse providing power to the acessories.
Am i making the mistake that it's not actually the 24vac i need to worry about (since the frequency is too quick for the coil to build enough inductance) but it's the 12v DC side that is causing the panel to eventually crash requiring a reset? Should i be placing the snubber network on the contact side then as a result?
Been at this for a few days and i'm trying to avoid running over to ChatGPT and further its plans for world domination.
Thanks
pops