generators

Thread Starter

muni

Joined Jul 29, 2008
45
sir in this attachment please find the question 12 and 13. i'm unable to understand how the answer has been derived. if any one can help me, i'm thanking them in advance
 

Attachments

vetterick

Joined Aug 11, 2008
35
Yes, phase shift is indeed the answer, you can only directly add AC voltages that are in phase with each other.

Question #12 looks like a stepper motor, I don't see any real practical use for it as a generator, but it works to show how much voltage is lost with the configuration.

Question #13 is a standard 3 phase generator, the generator actually generates 1.73 (square root of 3) times the output voltage, seems a little bit non productive, untill you find the motor connected to it uses 1.73 times less amperage than a single phase one.
 

scubasteve_911

Joined Dec 27, 2007
1,203
12) Is a two-phase generator.. You should know that the phase will be 90 degrees out of phase, so you plot both 70Vrms signals as vectors. One is at 0degrees, the other at 90degrees. Then, you draw them head to tail, then draw a new vector from the origin. Do the trig, it works out to be 90Vrms.

13) Same idea as 12, except the angle is now smaller.

Steve
 

Thread Starter

muni

Joined Jul 29, 2008
45
12) Is a two-phase generator.. You should know that the phase will be 90 degrees out of phase, so you plot both 70Vrms signals as vectors. One is at 0degrees, the other at 90degrees. Then, you draw them head to tail, then draw a new vector from the origin. Do the trig, it works out to be 90Vrms.

sir considering phase vectors one at 0 degrees and another at 90 degrees, it becomes pythagorous formula.
just by going the values rather than it is rms or avg √(70^2+ 70^2) =√(4900+4900) = √(9800)

again i'm somewhere wrong, please help out
 

Ron H

Joined Apr 14, 2005
7,063
12) Is a two-phase generator.. You should know that the phase will be 90 degrees out of phase, so you plot both 70Vrms signals as vectors. One is at 0degrees, the other at 90degrees. Then, you draw them head to tail, then draw a new vector from the origin. Do the trig, it works out to be 90Vrms.

sir considering phase vectors one at 0 degrees and another at 90 degrees, it becomes pythagorous formula.
just by going the values rather than it is rms or avg √(70^2+ 70^2) =√(4900+4900) = √(9800)

again i'm somewhere wrong, please help out
Your answer agrees with the answer in your pdf file. What's the problem?:confused:
 

Thread Starter

muni

Joined Jul 29, 2008
45
12) Is a two-phase generator.. You should know that the phase will be 90 degrees out of phase, so you plot both 70Vrms signals as vectors. One is at 0degrees, the other at 90degrees. Then, you draw them head to tail, then draw a new vector from the origin. Do the trig, it works out to be 90Vrms.

13) Same idea as 12, except the angle is now smaller.

Steve
sir thank you. i too have not noticed answer before asking you reply. i thank ron H sir also for his valuable suggestion.
now my doubt is in Q12 it was only 2 vectors. but in Q13 there are 3 vectors. how should i do it ? first shall i calculate the third vector with any one of them. and should i go to final calculation?
 

scubasteve_911

Joined Dec 27, 2007
1,203
Question 13 asks "how much voltage would be measured between any two open wires?"

So, there are 3 pole pairs, thus 360/(3*2) spacing between phases, or 60 degrees. Use trig. to solve for the resultant vector.

Steve
 

Thread Starter

muni

Joined Jul 29, 2008
45
Question 13 asks "how much voltage would be measured between any two open wires?"

So, there are 3 pole pairs, thus 360/(3*2) spacing between phases, or 60 degrees. Use trig. to solve for the resultant vector.

Steve
sir thank you, with this i got the funda of this question. sir i think if there are more no. of pole pairs, then the spacing between the phases will be by the formula 360/(n*2). if any thing wrong, please diect me
thank you sir
muni
 

scubasteve_911

Joined Dec 27, 2007
1,203
muni,

A little advice, try not to rationalize with formulae, try to be able to reason to a formula. This is because, a lot of times, a variable is changed and your handy formula sheet is no longer valid. For example, what if one were to make the windings asymmetrical or have more poles on the rotor?

Steve
 

DrNick

Joined Dec 13, 2006
110
Both of these questions are intended to test knowledge of polyphase systems. Both are essentially asking:

"what is the line voltage of a N phase system, given that the phase voltage."

question 12 is a N=2 phase system so

Vline=Vphase*sqrt(2)=70*sqrt(2)=98.99

question 13 is a N=3 phase Wye so:

Vline = Vphase*sqrt(3)=70*sqrt(3)=121.24
 

Thread Starter

muni

Joined Jul 29, 2008
45
Both of these questions are intended to test knowledge of polyphase systems. Both are essentially asking:

"what is the line voltage of a N phase system, given that the phase voltage."

question 12 is a N=2 phase system so

Vline=Vphase*sqrt(2)=70*sqrt(2)=98.99

question 13 is a N=3 phase Wye so:

Vline = Vphase*sqrt(3)=70*sqrt(3)=121.24
sir i really thank you. it gave me a very good idea about this.
 

scubasteve_911

Joined Dec 27, 2007
1,203
Okay, now I give you the same three phase generators with a single phase missing. Now it is assymetrical and you can no longer use simplistic formulae.

Always derive from first principals, it will come back to haunt you one day.

Steve
 