Fuses and Circuit breakers
Biggsy100
Joined Apr 7, 2014
88
Hi, please could someone have a read through my mini report and critiq as need be.
It does need editing and prettying up, but for now i'd like to focus on the highlighted detail. Many thanks
bertus
Joined Apr 5, 2008
22,999
I did not say it is bad.
On the first page the drawing is not shown correctly.
Also the text in the symbols are splt or going through the symbols.
Text and the drawing are running over each other making the text unreadable.
33,123
Circuit breakers and fuses, unless installed on the equipment, are generally intended to protect the wiring and not the equipment. Think about it -- the circuit breakers are installed in the facility independent of what will eventually be connected as a load, which might change many times over the life of the circuit. Consider your home. Most of your circuits are probably on 15A breakers. Yet most of the things that you plug into them will be destroyed long before they reach 15A of current draw.
Your calculation work largely supports this view.
As for your calculations, some of them don't make a lot of sense. You seem to be starting off saying that you want a load capacity of 12MW (12,000kW) from a single phase supply of 400kV. Sounds excessive, doesn't it. But let's go with it. You then get that you need to support 30A of current in order to provide the desired load capacity. Okay. You then say that you want to size the wire so that the needed current capacity is only 80% of the wire's ampacity. Okay. But then you take the maximum load that you NEED to be able to deliver to your load, namely the 30A, and multiply THAT by 80% to the a maximum loading of 24A. What gives? If your maximum loading is 24A, then you can't deliver the 30A that you are designing for!
In the next line, you switch to 12kV instead of the 400kV you used in the initial computation. Why the change?
Biggsy100
Joined Apr 7, 2014
88
ok I see, below is the initial question I am working on. As I have already mentioned there are some mistakes. It is purely in it's skeleton phase until I get some 'meat on it' so to speak. I just need to know if it is heading in the right direction.
design a suitable protection system for a 12 kW load. The installation is supplied from a 400 V source having a measured impedance of 0.040 W that can be assumed worst-case. Your design solution should comprehensively include:
· Relevant design calculations,
· Details of the chosen protection system
· The design outcomes,
· The implications for the circuit cables to be used,
· Any assumptions made.
panic mode
Joined Oct 10, 2011
5,207
I stopped reading after second or third sentence. it states two reasons and then it lists one (ugh... that's a downer).
short circuit is not a reason for CB to trip if circuit is not connected to power yet (how is CB supposed to trip in this case?). overcurrent is a reason so everything mentioned in that second sentence is basically same thing. I would choose wording more carefully.
not sure if there was mention of any practical factors such as cost (fuses are MUCH cheaper than CBs), reliability (CBs are not as reliable as fuses), performance (CBs rarely if ever have same fault current rating as fuses), acceptance (much easier to get fuses with needed approvals), etc. then there is another one - no easy distinction between CBs and supplementary protection.