DC shunt used to measure current on AC mains

LesJones

Joined Jan 8, 2017
4,190
You could use it but I think you will have problems finding an AC meter with 75 mV full scale deflection. (And no you can't just put a bridge rectifier between the shunt and the meter as a bridge made from silicon diodes does not conduct until there is about 1.4 volts on it's input.) You would normally use a current transformer instead of a shunt to measure AC current.

Les.
 

Thread Starter

van53

Joined Nov 27, 2011
67
Thank you. I plan to use a digital multimeter to measure the voltage drop across the shunt to determine the current. Why is it that these shunts are only advertised as DC such as these:

http://canada.newark.com/canadian-shunt/la-15-100/shunt/dp/74K0482

Is it because they are mainly used in parallel with DC analog panel meters ?

Would a current transformer be more or less accurate vs a shunt when measuring AC mains current?
 

Thread Starter

van53

Joined Nov 27, 2011
67
For the shunt I had just linked, I noticed there was a comment from a customer which stated:

Questionable For AC Use?
we are using this in a high frequency setting, and on initial use, our calculations were not turning out as expected, it could be due to the frequencies.

I am guessing that for AC 60hz it is fine but at high frequencies there could be issues?
 

Reloadron

Joined Jan 15, 2015
7,517
On eBay there are several shunts advertised as DC such as this:

https://www.ebay.ca/itm/DC-75mV-15A...870039?hash=item419e400557:g:rpgAAOSwo6lWHk5E

Can such a shunt be used on AC mains (USA) to determine current for a given circuit? Or is there a different type of shunt used for AC?
If it can be used on AC mains, should the specifications remain the same (i.e. 75mV @ 15A ) ?
How much AC current are you looking to measure? That's where it all begins. Can a current shunt like what you have looked at be used to measure AC current? Yes, but measuring the low level AC voltage dropped across the shunt becomes a little difficult. Depending on the current level you wish to measure there are other AC current options.

For the shunt I had just linked, I noticed there was a comment from a customer which stated:

Questionable For AC Use?
we are using this in a high frequency setting, and on initial use, our calculations were not turning out as expected, it could be due to the frequencies.

I am guessing that for AC 60hz it is fine but at high frequencies there could be issues?
The higher the AC frequency the more problems that can arise on the measurement plane.

So how much AC current? I assume you just want a basic Average responding RMS indicating measurement? The difference depends on the load you have. Additionally if this is just a simple home type project then I doubt you need an expensive solution but if this is an industrial type project where accuracy is paramount then things change.

Ron
 

Thread Starter

van53

Joined Nov 27, 2011
67
How much AC current are you looking to measure? That's where it all begins. Can a current shunt like what you have looked at be used to measure AC current? Yes, but measuring the low level AC voltage dropped across the shunt becomes a little difficult. Depending on the current level you wish to measure there are other AC current options.


The higher the AC frequency the more problems that can arise on the measurement plane.

So how much AC current? I assume you just want a basic Average responding RMS indicating measurement? The difference depends on the load you have. Additionally if this is just a simple home type project then I doubt you need an expensive solution but if this is an industrial type project where accuracy is paramount then things change.

Ron
I am looking to load the mains as close as possible to 15A without tripping the breaker (perhaps a 20A shunt may be better). I am assuming that since I am measuring 60hz sine-wave mains it wouldn't make any difference if I use an average responding meter vs a true rms meter?

This is just a simple home project. I want to record the voltage before and after the load (along with current draw) so that I can calculate the neutral to live loop impedance to obtain the prospective short circuit current for a given outlet.
 

Reloadron

Joined Jan 15, 2015
7,517
From our friends at Keysight:
True RMS responding multimeters measure the "heating" potential of an applied voltage. Unlike an "average responding" measurement, a true RMS measurement is used to determine the power dissipated in a resistor. The power is proportional to the square of the measured true RMS voltage, independent of waveshape. An average responding ac multimeter is calibrated to read the same as a true RMS meter for sinewave inputs only. For other waveform shapes, an average responding meter will exhibit substantial errors as shown in the figure to the right.

A multimeter typically uses a dc blocking capacitor to only measure ac component of a signal. Only the "heating value" of the ac components of the input waveform are measured (dc is rejected). For sinewaves, triangle waves, and square waves, the ac and ac+dc values are equal since these waveforms do not contain a dc offset. Non-symmetrical waveforms, such as pulse trains, contain dc voltages, which are rejected by ac-coupled true RMS measurements.
Likely if you just want to measure US mains power an average responding setup will get you close enough. The load is what determines what you want but for a true sine wave general use an average responding RMS indicating system would be fine. When considering a shunt if you expect a 15 amp load then consider a 20 amp shunt, when run at their limits shunts, especially cheap shunts heat and as they heat their resistance changes and your measurement degrades.

For 120 Volt 60 Hz mains power I would not use a shunt. I would use either a CT (Current Transformer) or an AC Current Transducer with a DC out proportional to the AC current. The only times I used a resistive shunt to measure AC it was 1.0 Hz and below. They simply are not practical for AC current measurement but nothing says if you find a good scalable AC low voltage meter you can't use one.

Current transformers are popular for measuring AC current in less costly manners,

Coil 3.jpg

Here is a current transformer opened up, Your main current carrying conductor gets looped through the donut hole..and the output is from the secondary wires, black and white,

Coil 1.jpg

They make 5 amp input ac meters which can be scaled to the current transformer connected to it.

Finally they make AC Current Transducers which outout a DC voltage or current which is proportional to the measured current,

CT2.jpg

So there is a wide variety of choice dependig on what your piggy bank allows. One time test curcuit go cheap, long time monitoring and recording data then things can get pricey,

Ron
 

Thread Starter

van53

Joined Nov 27, 2011
67
For 120 Volt 60 Hz mains power I would not use a shunt. I would use either a CT (Current Transformer) or an AC Current Transducer with a DC out proportional to the AC current. The only times I used a resistive shunt to measure AC it was 1.0 Hz and below. They simply are not practical for AC current measurement but nothing says if you find a good scalable AC low voltage meter you can't use one.
I was planning to use my Fluke 8050A to measure the voltage across the shunt. The resolution on the 200mV AC range is 10uV with an accuracy of 1%+10 (45hz). I calculate the potential error when measuring 15A would translate into 150mA. Would using a current transformer or ac current transducer with dc out provide better accuracy?
 

Reloadron

Joined Jan 15, 2015
7,517
No, as long as you have a Fluke 8050 available I would just use a shunt and see what you get. You should be able to find a 50 Amp / 50 mV shunt as they are real common or other shunt with 1 mV / Amp output. I also see Amazon has 50 Amp 75 mV shunts for a few bucks. So you figure 1.5 mV per Amp.

Funny you mentioned that meter as the model number sounded familiar. I have one of those in a pile of old stuff in the basement. :)

I would start with just adding an inexpensive shunt and see what you get doing it that way. The CTs and AC current transducer solutions can get a little pricey. Also when using a shunt, if possible, place it in your neutral leg just in the best interest of safety. In a DC solution it would be called measuring the Low Side current.

Ron
 

MrAl

Joined Jun 17, 2014
11,474
Hello,

Just a quick note as much has been said already that would help.

Choosing a 75mv shunt isnt that good of an idea unless you have to. The reason is because it is harder to convert voltage to current in your head when taking readings. Sure you can do it, but with a 50mv or 100mv shunt it is much easier.

For example, with a 75mv 50A shunt, when the voltage reads 15mv what is your current?
Now, with a 50mv 50A shunt, when the voltage reads 10mv what is your current?
And now with a 100mv 50A shunt, when the voltage reads 20mv what is your current?

Notice the 50mv 50A shunt is easiest to read without even thinking because whatever you read in millivolts, that is the current in amps present.

Meters that read down into the 10's of microvolts work better for shunts as you probably already figured out. It's also a good idea to use a small RC filter if you plan to use a scope with it.

Shunts are not perfect, so you might calibrate yours with a regular current meter before you start taking readings.
 

MisterBill2

Joined Jan 23, 2018
18,503
Using a shunt and an RMS ac voltmeter to measure AC current through the shunt will certainly work, but the math will be a bit tedious, depending on the exact shunt ratings. And for your application it can work to use heaters and light bulbs as the loads. Determining the source impedance of your electrical system will be an interesting exercise. Good luck with the project, please post the results that you find.
 

Lundwall_Paul

Joined Oct 18, 2011
236
To answer your question. The shunt on eBay they should drop the "DC" from the description. I have used similar shunts on both AC and DC. Never used them on mains and wouldn't use them on mains. I would go for a current transformer.
 

MisterBill2

Joined Jan 23, 2018
18,503
A resistive shunt will work well on mains circuits, but of course making everything safe can be a big chore. But I have quite a few shunts and only two current transformers. And only one nice ammeter to use with a shunt on AC.
 

Thread Starter

van53

Joined Nov 27, 2011
67
I ended up purchasing a 20A 50mV shunt +/-0.25% (data sheet linked here). I am curious on what is the best practice for taking measurements and making calculations using a shunt. As the shunt has a very low resistance its effect on my intended circuit (target 15A draw on mains using appliances which would be equivalent to an 8ohm load) would be minimal.

Lets say you read 37.5mV across the shunt does one use the shunts rating (i.e. 50mV@20A +/-0.25% [5mV per amp]) to determine the current in the circuit which in this case would be 15A? Or is the best practice to take into consideration the very minimal effect the shunt has on the circuit (its reduction on the current) and using the measuring voltage and measured resistance of the shunt calculate the current going through the circuit?
 

crutschow

Joined Mar 14, 2008
34,432
Or is the best practice to take into consideration the very minimal effect the shunt has on the circuit (its reduction on the current) and using the measuring voltage and measured resistance of the shunt calculate the current going through the circuit?
You could, but it has what would generally be considered a negligible effect on the load current (perhaps 0.04% in a 120V circuit).
 

WBahn

Joined Mar 31, 2012
30,058
I am looking to load the mains as close as possible to 15A without tripping the breaker (perhaps a 20A shunt may be better). I am assuming that since I am measuring 60hz sine-wave mains it wouldn't make any difference if I use an average responding meter vs a true rms meter?
It's not the frequency that matters (up to a point), but rather the waveform. If your current waveform (not voltage waveform) is a sinusoid, then you can use either an true RMS or an average responding but RMS indicating meter and you will get the same results. But if your load draws a non-sinusoidal current, as many do, then your average responding meter may give nearly useless results.
 

Thread Starter

van53

Joined Nov 27, 2011
67
You could, but it has what would generally be considered a negligible effect on the load current (perhaps 0.04% in a 120V circuit).
Thank you. I'll use the marked value (20A@50mv) in this case to calculate the current draw.

Based on some of the above suggestions to use a current transformer, I also picked up a 20:5 CT (model 189-020 data sheet here)
The markings on the CT is Class 0.6 B0.2 50-400Hz.

I am curious how the readings of the shunt vs the CT will compare. I am planning to use the shunt and CT together in series at the same time so I can compare readings at once.

From what I've read online in terms of CT markings is that my CT will have an accuracy of 0.6% when a burden resistor not greater than 0.2ohms is placed on the secondary, is this correct? The CT in question does not have a window. The data sheet indicates "Window Size: Wound Primary". Would my CT be considered a bar type or wound CT, or something else?

But if your load draws a non-sinusoidal current, as many do, then your average responding meter may give nearly useless results.
I'm planning to use a true RMS meter, however now I am wondering if the load (heater circuitry) draws a non-sinusoidal current then will it cause an issue for my CT as it is rated between 50-400hz ? The loads I was planning to use were oil based heater or micrathermic heater and various light bulbs to get close to 15 amps. In this case I suppose I could view the waveform on an oscilloscope across the shunt.
 

MisterBill2

Joined Jan 23, 2018
18,503
If you are setting the current in the circuit then the exact voltage does not matter. It is the current that develops the voltage drop that will allow you to figure the resistance in the line. I you chose to be redundant then you could use two shunts and calculate the current based on the readings from each of them. Because you are controlling the current the effect of the shunt resistance does not matter at all, unless it is so large that it limits the current.
 

Reloadron

Joined Jan 15, 2015
7,517
Lets say you read 37.5mV across the shunt does one use the shunts rating (i.e. 50mV@20A +/-0.25% [5mV per amp]) to determine the current in the circuit which in this case would be 15A?
You have a 20 amp shunt which outputs 50 mV full scale at 20 amps. That should be 0.0025 (2.5 mV ) / Amp. Not 5 mV / Amp but yes. 37.5 mV would be 15 amps.

As to the CT rather than run a wire through the primary they have a bar centered in the primary with brass nuts, that is fine. So 20 amps flowing through the primary results in 5 amps flowing through the secondary. Keep in mind these transformers are designed to work into, as you mentioned, a very low burden resistance. Also, it is very unwise to use a CT of this type with an open secondary as extremely high voltages will exist. Do not run that CT open circuit on the secondary. Here is an old thread about CT open secondary high voltage.

As to your mention of heaters as a load. Heating elements are a resistive load but when combined with for a blower motor you have resistive and inductive which is pretty common in a household load.

Ron
 