Yes, as well as the supplying circuit breaker.Or do I also need to change the connecting wires for this purpose?
Yes and what I see pictured is not US, beats me but it isn't US or anything I have seen in N. America.I'm not familiar with US code, but I think if you want all four outlets to be 16A then you will need to upgrade the outlets, the wiring that feeds the outlets, and any circuit breakers/fuses that protect the wiring.
I'm not familiar with US code, but I think if you want all four outlets to be 16A then you will need to upgrade the outlets, the wiring that feeds the outlets, and any circuit breakers/fuses that protect the wiring. If you wnat to replace the four outlets with a single outlet then the wiring/breakers should already be rated to cope with that, unless each outlet is separately wired from the distribution box and has its own breaker.
US outlets are typically 15A (14 AWG) or 20A (12AWG) supply. Outlets for 20A usually have the extra 90° tab option.This obviously isn't the US for two reasons.
1. That is not a US receptacle.
2. I don''t know anywhere in the US where someone has a 6A service. I am pretty sure minimum is 20A.
And shouldn't the "electron_prince" know the answer to this question?
6amps is the limit per house hold.!Looks like India or South Africa crossed with something else?
Max, next time you are in my neighborhood taking pictures please stop and we can have a beer or two.6amps is the limit per house hold.!
Max.
US outlets are typically 15A (14 AWG) or 20A (12AWG) supply. Outlets for 20A usually have the extra 90° tab option.
View attachment 148033
Is that you wiring up another service to your house? I knew things were bad in Cleveland but I had no idea.Max, next time you are in my neighborhood taking pictures please stop and we can have a beer or two.
Ron
Whatever it takes for mo power, I needs mo power.Is that you wiring up another service to your house? I knew things were bad in Cleveland but I had no idea.
Things may improve a little in September. I heard they will add another tierod to the grid.Is that you wiring up another service to your house? I knew things were bad in Cleveland but I had no idea.
Yes, this is not of US but Indian.This obviously isn't the US for two reasons.
Because these outlets were meant for phone charging, using a small vacuum cleaner and other such stuffs. And for such purpose in India, we usually have 6A outlets only. There are other outlets that are meant for ACs and they are rated 25 amps but since I have installed the AC in a different location I need to use these outlets with 6A rating.How do you know your outlets are rated for 6A?
Not per household. I think it's the rating of that socket. If we draw more current then that from that particular socket then it probably will burn out or something might happen. The overall limit should be high because we have other 25A outlets in bathrooms and in all rooms. They come paired with MCBs. So if they have provided that arrangement then I am sure that the total current to the house should be definitely more than that.6amps is the limit per house hold.!
Max.
Yes, I think that's what I need to do. I thought I might save some money by doing it myself as it appeared like a simple task initially.Back to the original question:
If your outlet is not rated at a high enough current you probably need to get help from a licensed electrician.
If you need 15 or 20 amp service for the air conditioner, not only the outlet but also the supply wiring and circuit breaker must be suitable for that current rating. I don't know what wire gauge is used for 6 amp service, but since wire size has been set by heating and temperature rise, it will not be safe if you are running 16 amps through it. And I am thinking that it is 200, or perhaps 230 volts, as found in the UK, which is where I have seen that style of outlets. So you have a fair sized project ahead in order to have safe and reliable power.If each of them outlets are 6 amps each I bet the wiring is not a problem.
breaker probably to small.
Only way to no is to see the wire size and check the breaker.
It was tongue-in-cheek!Not per household. I think it's the rating of that socket. If we draw more current then that from that particular socket then it probably will burn out or something might happen.
.