Hi,
I will try to be short. I'm running LF off-grid PV inverter (Victron). When the battery is full, I want to use a resistive load (heater element) as the dump load. No problem there. But I've started thinking about how to regulate the load and I'm finding conflicting claims. I will probably start with what I would like to achieve.
Regulation resolution: Ideally I would like to be able to regulate the load in let's say 50 W increments. So just using multiple heating elements or combining them with some relay logic isn't going to cut it. When I have a 950 W surplus in the winter I want to use nearly all energy, not to be in a position where I can only switch load with 500 W increments.
Grid impact (microgrid): Because my power source is the PV inverter in off-grid mode it isn't as hard of a supply as the power grid. So I want a regulation that won't generate any or a minimal amount of flicker, EMI, transients etc. I don't want any kind of regulation that would be "hard" on the PV inverter. The reason is to minimise any stress on the inverter for the sake of its working life.
The types of regulation I've considered:
Autotransformer: bulky, pricy, slow to regulate+ need to motorized control
VFD: I was expecting this to be the best solution but apparently VFD used for only resistive load could be problematic. Also, VFD for bigger loads (3 kW+) for only 1 phase are really pricy. If we are talking about something from a more reputable manufacturer than some noname knockoff from China.
Phase angle regulation (SSR): The regulation resolution should be ideal but the impact on the grid needs to be also considered. It will send a lot of... unwanted things back to the microgrid.
Zero-cross regulation (SSR): The sources are 50/50 on this. I would expect there would not be any substantial impact on the grid because the switching takes place at zero but some people claim it causes a lot of flicker. It also probably isn't "soft" on the power supply either.
PWM (AC chopper): Probably the winner for me, but feel free to change my mind. Chopping the AC at let's say 50 kHz should allow for smooth regulation resolution, the higher frequency should also allow for smaller filtering elements at the input of the regulator and it shouldn't be that hard to implement. But I didn't have much luck finding any reference designs or something to be inspired by. Do you agree this is the way to go or are there any better opinions? In the same price range, I might add. (The VFD solution from Danfoss would cost even more than the PV inverter so that is the reason I'm mentioning the price.)
I will try to be short. I'm running LF off-grid PV inverter (Victron). When the battery is full, I want to use a resistive load (heater element) as the dump load. No problem there. But I've started thinking about how to regulate the load and I'm finding conflicting claims. I will probably start with what I would like to achieve.
Regulation resolution: Ideally I would like to be able to regulate the load in let's say 50 W increments. So just using multiple heating elements or combining them with some relay logic isn't going to cut it. When I have a 950 W surplus in the winter I want to use nearly all energy, not to be in a position where I can only switch load with 500 W increments.
Grid impact (microgrid): Because my power source is the PV inverter in off-grid mode it isn't as hard of a supply as the power grid. So I want a regulation that won't generate any or a minimal amount of flicker, EMI, transients etc. I don't want any kind of regulation that would be "hard" on the PV inverter. The reason is to minimise any stress on the inverter for the sake of its working life.
The types of regulation I've considered:
Autotransformer: bulky, pricy, slow to regulate+ need to motorized control
VFD: I was expecting this to be the best solution but apparently VFD used for only resistive load could be problematic. Also, VFD for bigger loads (3 kW+) for only 1 phase are really pricy. If we are talking about something from a more reputable manufacturer than some noname knockoff from China.
Phase angle regulation (SSR): The regulation resolution should be ideal but the impact on the grid needs to be also considered. It will send a lot of... unwanted things back to the microgrid.
Zero-cross regulation (SSR): The sources are 50/50 on this. I would expect there would not be any substantial impact on the grid because the switching takes place at zero but some people claim it causes a lot of flicker. It also probably isn't "soft" on the power supply either.
PWM (AC chopper): Probably the winner for me, but feel free to change my mind. Chopping the AC at let's say 50 kHz should allow for smooth regulation resolution, the higher frequency should also allow for smaller filtering elements at the input of the regulator and it shouldn't be that hard to implement. But I didn't have much luck finding any reference designs or something to be inspired by. Do you agree this is the way to go or are there any better opinions? In the same price range, I might add. (The VFD solution from Danfoss would cost even more than the PV inverter so that is the reason I'm mentioning the price.)