30 mils? Do you mean 30 minutes?if it exceeds the 1.7 amps, after( 30 mils) it will break the circuit.
30 mils? Do you mean 30 minutes?if it exceeds the 1.7 amps, after( 30 mils) it will break the circuit.
I don't quite understand, any and all currentl will be 'seen' by the current limit at all times.I am aware about the initial current that is present. This is why the limit of the current is processed before the relay and before the motor.
I meant 0.3 seconds30 mils? Do you mean 30 minutes?
Yes, that is right... Again I.m just trying to measure from the C.T with comparator op amp and further to broke the circuit if it exceeds the value. I.m sorry Max but I don't quite understand what are you asking.I don't quite understand, any and all currentl will be 'seen' by the current limit at all times.
Max.
P. S. there may be needed a longer time, you are right.Yes, that is right... Again I.m just trying to measure from the C.T with comparator op amp and further to broke the circuit if it exceeds the value. I.m sorry Max but I don't quite understand what are you asking.
I would tell anybody within earshot that they can't expect me to do my job if I don't have access to ALL of the available information, and I would interpret the second statement with a jaundiced eye. Just because somebody tells you something doesn't make it true. In this case I think there is ample evidence to conclude that you are maybe being misled. If you choose to be misled, then that is on you. If you have some way of ascertaining the veracity of what you have been told -- so much the better. You are absolutely doing your job. Believing what you have been told could be interpreted as negligence in some professional settings. Guess who takes the fall between an intern and a supervisor? Engineering is about knowing what you are doing so well that you can defend every action in a court of law.Unfortunate I don't have any access to the motor information. Been told that it operates in these margins and that is all. ....
That's a very good point. We don't even know for sure if this motor is being manually controlled by e.g. a three wire start-stop arrangement or if it is part of an automated control scheme. Generally speaking, motor overload protection (and undervoltage drop-out) always requires some sort of human interaction to permit re-starting of the motor after an overload has occurred. The only real exception to this is with small motors that are completely enclosed or guarded in such a way that an unexpected start up cannot possibly cause injury (e.g. self contained direct-drive air compressor pumps, etc.).Is auto-reset an important feature here? So that it doesn't require being manually reset after an overload situation? That presents its own dangers - such as a stopped motor starting unexpectedly.
I hope they don't expect the "intern" to quickly pull something out of a dark place, because I think we have just given him at least a years worth of important questions to run down. If they are willing to pay him to do that for a whole year, it would be real "helluva deal" for him. Oh wait....is this a paid internship or is he working for free..,ah, I mean ancillary benefits?That's a very good point. We don't even know for sure if this motor is being manually controlled by e.g. a three wire start-stop arrangement or if it is part of an automated control scheme. Generally speaking, motor overload protection (and undervoltage drop-out) always requires some sort of human interaction to permit re-starting of the motor after an overload has occurred. The only real exception to this is with small motors that are completely enclosed or guarded in such a way that an unexpected start up cannot possibly cause injury (e.g. self contained direct-drive air compressor pumps, etc.).
Usually the latter rely on a bi-metal thermal switch embedded in the windings, whereas everything else relies on either pushbutton-type thermal-only circuit breakers or entirely separate motor overload protection.
What kind of motor are we dealing with? A custom number designed to fit into an appliance - or a NEMA/IEC/etc. standard frame size that can be ordered with an internal overload protector built-in?
We really need to see the motor nameplate here. When sizing anything for motors, we generally need to know horsepower (kW), voltage, full load amperage, phase, frequency, rated speed, service factor, duty rating, temperature rise, locked rotor kVA, NEMA design (if applicable) and any other "special" information such as whether it is rated for use in classified locations (explosion-proof), requires an auxiliary blower, is rated for VFD service or is fitted with a dehumidifier/heater, etc.
"Sketchy" is the only word that comes to mind to describe this situation. If I was the intern, I'd be running, not walking away as fast as possible.The bottom line, IMO, is that an "Intern" should not be responsible for creating "a small system that will take place of the fuse highlighted".
Any attempt at this project should be overseen and OK'd by qualified superiors to ensure compliance with safety and current regulations.
From the DWG style and the voltages shown, the OP may not be under N.A. jurisdiction of NFPA79/70.
But I am am sure that they most likely have to conform to some equivalent body.
Max.
As I mentioned in post #9, if it is fusing, it is not allowed, if a DP breaker it can be used, but not usually recommended.Looking at the diagram in post #1 where it has a designation of F1 it looks to be switching the Neutral. Do you really want neutral switched?