2 phases no neutral load

Thread Starter

Thank you

Joined Feb 20, 2019
4
I have a water heater ( 220 VAC ) which is only connected to two phases ( each phase is 110 VAC ) with no heater. I have never came across such connection, how does the circuit work ? Are there any source material I can read or wTch to learn about it ? And why such connection exists ?
 

MaxHeadRoom

Joined Jul 18, 2013
30,658
If you are in N.A. (USA), then a residential supply is not two phases , it is single-split phase. 120v-0-120v .
IOW it is fed from a single phase transformer.
The 0v is the neutral and is earth grounded at the transformer and the distribution panel.
No confusion.
 

crutschow

Joined Mar 14, 2008
38,504
I have a water heater ( 220 VAC ) which is only connected to two phases ( each phase is 110 VAC ) with no heater.
The 110Vac "phases" are the two hot sides from a single winding on the residential signal-phase transformer, which give 220Vac single-phase.
The 110Vac phases are simply each hot side to neutral, with neutral being the center-tap of the 220Vac winding.
This gives an apparent phase-shift of 180° between the two 180Vac lines.
Is it an on going argument is 240 single phase or two phase.
There should be no argument as the definitions are plain.
Two 120Vac phases that are 180° out-of-phase are split-phase.
True multiphase AC has phase-shift between phases that are other than 180°, such a 90° for 2-phase and 120° for 3-phase.
 

MaxHeadRoom

Joined Jul 18, 2013
30,658
And to add, a 3ph transformer is made up of three 1ph cores, so for 2 phases, 2 cores would be required.
When in fact the residential 120-0-120 version is provided by one single phase core.
 
Last edited:

Delta Prime

Joined Nov 15, 2019
1,311
And to add, a 3ph transformer is made up of three 1ph cores, so for 2 phases, 2 cores would be required.
When in fact the residential 120-0-120 version is provided by one single core.
The 110Vac "phases" are the two hot sides from a single winding on the residential signal-phase transformer, which give 220Vac single-phase.
The 110Vac phases are simply each hot side to neutral, with neutral being the center-tap of the 220Vac winding.
This gives an apparent phase-shift of 180° between the two 180Vac lines.
There should be no argument as the definitions are plain.
Two 120Vac phases that are 180° out-of-phase are split-phase.
True multiphase AC has phase-shift between phases that are other than 180°, such a 90° for 2-phase and 120° for 3-phase.
Right Church, wrong pew. :)
 

nsaspook

Joined Aug 27, 2009
16,321
And to add, a 3ph transformer is made up of three 1ph cores, so for 2 phases, 2 cores would be required.
When in fact the residential 120-0-120 version is provided by one single core.
I have 'real' 2-phase motors for cryogenic vacuum pump motors. A vendor installed the HE compressor drive system strapped for 3-phase motors. The 2-phase motor would run on two legs of 120 phase shifted power but was very noisy.