10kW 48V DC instant water heater

dl324

Joined Mar 30, 2015
16,845
Is your power supply capable of providing over 200 amps?

\(I=\frac{P}{V}=\frac{10KW}{48V}=208A\)

Are you competent to work with high power?
 

Thread Starter

davelondon

Joined Mar 30, 2021
21
My power supply is a 57kWh lithium battery bank, so 10kW is less than 0.2C, so should be fine (lithium batteries can usually safely be discharged at about 0.4C).

> Are you competent to work with high power?

Nope! But will get some help from someone who is before turning this system on.
 

Ya’akov

Joined Jan 27, 2019
9,069
My power supply is a 57kWh lithium battery bank, so 10kW is less than 0.2C, so should be fine (lithium batteries can usually safely be discharged at about 0.4C).

> Are you competent to work with high power?

Nope! But will get some help from someone who is before turning this system on.
KWh and KW are two different things. You need to know how much current your battery can provide.
 

Ya’akov

Joined Jan 27, 2019
9,069
Yes, but 1C for a 57kWh battery is 57kW... right?
The actual ability for the battery to deliver current is more complex than a simple C rating. You need to know things like ESR which will limit the delivery and derating due to heating. That simple conversion is just an estimate.

You need to know if the battery you want to use to generate 200A for a period as long as the heating element will need to run.
 

Thread Starter

davelondon

Joined Mar 30, 2021
21
These are the cells I'm using... This spec page lists 0.5C as the max discharge current:

https://www.evlithium.com/hot-lithium-battery/946.html

... so I'm confident that the battery pack I'm using will easily supply 10kW for the duration that it's needed...

Here's some chat about someone with basically the same battery pack as mine (4 x 1P16S) talking about internal resistance and heating... sounds like it's not a big issue: https://diysolarforum.com/threads/heat-build-up-at-0-125c-discharge-rate.13907/
 

Ya’akov

Joined Jan 27, 2019
9,069
These are the cells I'm using... This spec page lists 0.5C as the max discharge current:

https://www.evlithium.com/hot-lithium-battery/946.html

... so I'm confident that the battery pack I'm using will easily supply 10kW for the duration that it's needed...

Here's some chat about someone with basically the same battery pack as mine (4 x 1P16S) talking about internal resistance and heating... sounds like it's not a big issue: https://diysolarforum.com/threads/heat-build-up-at-0-125c-discharge-rate.13907/
The battery may be able to handle it, though I am not sure about long term. Another consideration is that you will need to run something like 2/0 AWG wire to the heating element. If you were running 480V you'd only need 20A and the conductors would be a much more reasonable size.

Whatever you do, PLEASE, be very careful and make sure the margins for safety are large. You are thinking about playing with a LOT of current. Make sure you get someone who knows such things to vet all of it.
 

Alec_t

Joined Sep 17, 2013
14,280
Whatever you use is going to be very expensive. In theory you could parallel a load of mains-rated 2kW immersion heaters. At 240V rating you'd need 25 x 5 = 125 to get 10kW at 48V !!!. Not very practical :(.
 

sagor

Joined Mar 10, 2019
903
These are the cells I'm using... This spec page lists 0.5C as the max discharge current:

https://www.evlithium.com/hot-lithium-battery/946.html

... so I'm confident that the battery pack I'm using will easily supply 10kW for the duration that it's needed...

Here's some chat about someone with basically the same battery pack as mine (4 x 1P16S) talking about internal resistance and heating... sounds like it's not a big issue: https://diysolarforum.com/threads/heat-build-up-at-0-125c-discharge-rate.13907/
Those cells you link to have a 280Ah capacity (at 0.5C). Running them at 200A will give just over an hour's worth of current at rated voltage - assuming you get everything together...
Also, that 280Ah rating is to a point where the cells drop to 2.5V, after which the battery is basically drained. That means your 3.2Vx15 = 48V will quickly become 2.5Vx15 = 37.5V. And, current will drop (as will the 10kW heat)
 

DickCappels

Joined Aug 21, 2008
10,153
I'll try to save you some time. Look for somebody who has already done this. If you can't buy it now, you probably won't be able to get it unless you are NASA. There is nothing ordinary about your request.
 
48 volts is an uncommon voltage for heating elements. 12V, 120V, 208V, and 240V immersion heating elements are off the shelf parts. Calculate the resistance of a few readily available heating elements and see if you can assemble them in a series/parallel arrangement that suits your needs.

Or just use a photovoltaic inverter to obtain 240VAC. I'm assuming by the fact that you *have* such a battery bank at your disposal that this is already part of an existing photovoltaic or peak-shaving system, which begs the question; why bother trying to heat water using DC? If inverter losses are a concern then adding more PV modules to compensate would be a far more economical and less laborious option than embarking on a venture such as this.
 
Last edited:

Thread Starter

davelondon

Joined Mar 30, 2021
21
Those cells you link to have a 280Ah capacity (at 0.5C). Running them at 200A will give just over an hour's worth of current at rated voltage - assuming you get everything together...
The system is composed of four independent 1P16S batteries in parallel... So each battery provides 52A.
 

Thread Starter

davelondon

Joined Mar 30, 2021
21
OK everyone, thanks for all you help. It seems like this will be too difficult / expensive so I'm cancelling this part of the project.
 