Zener Dioide Problem
Digit0001
Joined Mar 28, 2010
100
Hi
How would you do the following problem:
A Zener diode is connected in a voltage regulator circuit.
The Zener voltage is Vz = 10V and the Zener resistance is assumed to be rz=0. (a) Determine the value of Ri such that the Zener dioide remains in breakdown if the load current vari4es from Iload =50 to 500mA and if the input voltage varies from V1 = 15 to 20V. Assume Iz(min) = 0.1I(max).
P.S
t_n_k
Joined Mar 6, 2009
5,455
The constraints are minimal.
The minimum zener current would presumably occur when the input voltage is at its lowest and the load is at its maximum. You are advised to set Iz(min) to 0.1Iload(max). That should be sufficient information to solve the problem.
Digit0001
Joined Mar 28, 2010
100
i have tried doing this:
I1= Iz+Il
Iz = Vz/rz = 0
so I1 = IL
now (Vin(min) - Vz)/ Ri = I1 = IL(min)
(20 - 10)/ Ri = 50m
10/50m = Ri
so Ri = 200ohms
checked with answer this is wrong, what is wrong with this??
35,093
At max Iload, Rload = 10/.5 = 20 ohm
At max Vi Ri = 10/.5 = 20 ohm
If you need to include Iz, Rz = 200 ohm
Then Ri = 20//200 = 200/11 = 18 ohm
jimkeith
Joined Oct 26, 2011
540
Ri = ERimin /IRi
ERi min = 15-10 = 5V
IRi under above conditions = 0.5 + 0.1*0.5 = 0.55A
Ri = 9.09Ω
A better question is: Specify a zener that will do this without smoke
t_n_k
Joined Mar 6, 2009
5,455
Ri = ERimin /IRi
Ri = 9.09Ω
Agree with your value for Ri - hence my query.
Excellent point about the practical implications.