Voltage is 220VAC and length is about 30 meters Sir.Since you didn't say what voltage the motor operates at....*shrug* There's no way to know. The length of wire between to motor and power supply also makes a difference.
I’m so sorry for incomplete question Sir.The rating plate specifies 11.2A
Required size of cable will depend on many other factors - in order of importance:
1. The country in which it is being installed (regulations differ across the world)
2. The size of the circuit breaker or fuse that is protecting it.
3. The type of cable (armoured, twin-and-earth, flex etc.)
4. The temperature rating of the cable insulation.
5. How the cable is installed (in conduit, clipped to a wall, buried underground)
Based on British regulations it would probably be 4mm^2 for a 32A breaker (twin-and-earth, clipped direct)I’m so sorry for incomplete question Sir.
1. Country is Myanmar(Burma) and voltage rating is 220V.
2. Circuit breaker I am using is 32A.
3. Type of cable is single( our local electricians usually call it single and we have to use separated colors of two wires to install).
4.Temperature rating of the wire insulation is 75 degree Celsius.
5. I am planning to install by clipping on the wall.
Thank you for your additional questions.
1.5mm^2 would be sufficient for 11.2A.The next-larger Wire-Size would be a better choice because of the ~30-Meter distance.
Over a ~30-Meter distance, the Voltage-Drop in the Wire starts to become a significant factor.
Voltage-Drop can cause the Motor to over-heat when subjected to Heavy-Loads.
.
.
.
The name-plate voltage is 220 volts, the name-plate current is 11.2 amps. Based on the USA standards, which are based on wire heating versus insulation life, you could get away with US wire size #14, that had 15 amp circuit protection.Voltage is 220VAC and length is about 30 meters Sir.
The OP is using a 32amp breaker which by N.A. standards is not only not allowed, it would be considered dangerous using 1.5mm2 conductor.The name-plate voltage is 220 volts, the name-plate current is 11.2 amps. Based on the USA standards, which are based on wire heating versus insulation life, you could get away with US wire size #14, that had 15 amp circuit protection.
BUT to handle the starting current and the voltage drop, a better choice would be the US wire size #12, rated to use 20 amp circuit protection.
Since the circuit protection is a 32 amp circuit breaker , I suggest US #10 wire, used for circuits with 30 amp protection. #8 would satisfy US codes, but as the application is elsewhere, and the running current is much less, #10 will be quite adequate.
Unfortunately I do not have the conversion between wire gage and metric diameter handy, and so that would need to be researched elsewhere. In addition, an open-air installation will not suffer as great a temperature rise as wires in conduit.
Certainly the unthinking application of the code does not allow for any variations no matter what. But at some point it is reasonable to consider the actual situation, rather than just reading the script.The OP is using a 32amp breaker which by N.A. standards is not only not allowed, it would be considered dangerous using 1.5mm2 conductor.
Read post #10.
| Thread starter | Similar threads | Forum | Replies | Date |
|---|---|---|---|---|
| R | Pulse vs wire size | Technical Repair | 6 | |
| D | Wire size for use with 30A fuse? | General Electronics Chat | 8 | |
|
|
Wire size ! | General Electronics Chat | 47 | |
|
|
Is have larger wire size can make circuit braker trip more fast ? | General Electronics Chat | 31 | |
|
|
What's better wire size for surge arrester ? | General Electronics Chat | 3 |